MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Coverage Area by 2X Throw, or the Actual Area?

2/2/2026

5 Comments

 
I am attempting to tweak a set of calculations that is slightly over the curve.

When measuring/assigning an area of coverage for an individual sprinkler into a hydraulic calculation program I am told the area per sprinkler is the largest dimension x 2, not the physical area the sprinkler protects. This is because the required distribution of water will be based on the largest dimension regardless of the physical dimensions of area protected.

Comparison example:

1) Physical Area for Pendent Sprinkler coverage is 14 x 8 = 112 sqft
Flow determined by 112 sq ft x .10 gpm = 11.2 gpm

2) Largest Dimension x 2 determines area per sprinkler and area is 14 x 14 = 196 sqft
Flow determined by 196 sq ft x .10 gpm = 19.6 gpm

Thanks in advance for your opinion and code basis. 


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Dan Wilder
2/2/2026 07:52:53 am

Unless your sprinklers are residential, extended coverage, CMSA (sometimes) or ESFR, the SxL method is the correct approach.

One clarification, the SxL are two different calculated numbers for SSU/SSP. To find either, it is the greater number of:
The total distance between 2 sprinklers
The distance to a wall (sometimes obstructions) x2

Repeat for the branch line calculation. You would not just take the largest of the SxL and apply that to the second number.

For SSU/SSP
2019-13
10.2.5 for spacing requirements
19.3.3 for density requirements
Specific to your question - 27.4.2.6.2
27.2.4.7.1 for discharge requirements

Reply
NK
2/2/2026 08:26:44 am

There is nothing in NFPA 13 that limits the square footage used in CMDA hydraulic calculations, however contract documents, AHJ requirements, insurance requirements may dictate maximum allowable spacing be used for future modifications. If you use a smaller area than the maximum, make sure it's clearly indicated on the drawings and calculations, noted on the hydraulic placard/general information sign, and that the spacing throughout the building matches the spacing of the sprinklers in the remote area that you proved hydraulically (you can't calc to 196ft and space 225ft everywhere else without additional calculations).

Reply
DG
2/2/2026 11:20:23 am

Definitely the largest of x2 dimension is what determines the area per sprinkler (so in your comparison example the coverage area is 196sqft not 112sq ft). I won't repeat good points already stated; however wanted to add one. If you have a OH occupancy, based upon the example you gave, you would end up with two heads in that small compartment vs one as the coverage area exceeds 130sqft.

Comparison example:

1) Physical Area for Pendent Sprinkler coverage is 14 x 8 = 112 sqft
Flow determined by 112 sq ft x .10 gpm = 11.2 gpm

2) Largest Dimension x 2 determines area per sprinkler and area is 14 x 14 = 196 sqft
Flow determined by 196 sq ft x .10 gpm = 19.6 gpm

Reply
Wes
2/2/2026 11:40:48 am

DG, in your 14 x 8 example, where does this requirement originate?

In concept, I understand that throwing 7-ft in either direction to cover 14 foot, with a sprinkler that deflects in a conical pattern, logically would be 14 x 14 ft; but what's the standard or code basis to doing so?

Technically (I wouldn't) someone could say that in order to throw 7-ft to one side, you can achieve that with an equivalent area (round circle) of 153.9 sqft (pi * 7-ft ^2). No one does that, but if we're making an argument that the THROW of the sprinkler needs to be accommodated so we're taking the larger distance twice (14 x 14), that's also a mathematical equivalent.

If a sprinkler covers 112 sqft actual or 112 S x L sqft calculated, what requires us to calculate an area of 196 sqft for a density?

I may have missed it, but I'm not familiar with a section of NFPA 13 that spells out the longest-throw distance and squares it for the density calculation.

Reply
Brett
2/2/2026 02:19:08 pm

Wes, the general spacing rules are in section 9.5.2.1 in the 2019 edition of NFPA 13. Dan pointed out the other applicable sections above (although there is a typo - 27.4.2.6.2 should be 27.2.4.6.2) and the fact that some sprinkler types have different spacing rules that override 9.5.2.1.

One thing I will add is that if the sprinklers you're calculating are in a small room (which has a definition in chapter 3) then the coverage area of those sprinklers is the area of the room divided by the number of sprinklers. That's in section 10.2.4.1.2.1 in NFPA 13 2019 edition.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT