Is the installation form of the control valve for the hydrant correct/allowed as shown?
It is a wet barrel hydrant, and the owner wants to save costs by installing the control valve directly below the hydrant. How should the effective coverage area of the fire hydrant be considered? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/27/2025 06:37:47 am
From NFPA 24 (2025 Edition) Chapter 7: Hydrants
Reply
CESAR LIRA
6/27/2025 02:21:43 pm
This can't do it. because the hydrant has a own gate in the elbow,. if there a different hydrant the gate valve could be a problem for the walkers
Reply
Dan Wilder
6/27/2025 08:12:44 am
I would argue "Not Allowed" as this creates an obstruction to the operation of the hydrant for a responding crew for 360° clear access.
Reply
Chad
6/27/2025 08:48:47 am
Agreed-
Reply
Anthony
6/27/2025 09:45:30 am
I agree with Dan and Chad here about the creation of an obstruction and a car problem. It just looks like it creates more problems than it solves.
Reply
Glenn Berger
6/27/2025 08:14:42 am
For a WET BARREL Fire Hydrant this appears to be legit from an NFPA standpoint. Might want to check the applicable OSHA requirements. If no guard posts are present on all sides as the Gate Valve will be a protruding item at a low elevation.
Reply
Jack G
6/27/2025 12:18:30 pm
The hydrant may not work properly work mounted directly to the bottom of a hydrant . The stem of the hydrant moves up and down to open and close. When closed it moves past the weep holes that allow drainage of the hydrant. This feature may not work.
Reply
Jesse
6/27/2025 02:34:36 pm
Prior to working in fire protection engineering and loss control, I was a career Firefighter / Medic for 19 years. I would really, really not like this idea. Wrapping the hydrant alone to lay LDH supply line could be a train wreck.
Reply
CESAR LIRA
6/27/2025 02:40:34 pm
Completely agree
Reply
Ryan Hinson
7/2/2025 11:26:58 am
Some responses above appear to be confused as to the indicated type of hydrant. The hydrant in question is a wet-barrel (Jones 3760-series) hydrant. This hydrant type has no vertical 'stem' from a top nut to a base valve (dry-barrel) since, by definition, this hydrant is flooded and under pressure with each individual hose connection valves necessarily preventing water flow. There is therefore, no intrinsic internal universal hydrant 'control' (shutoff) valve in the base of this configuration...which must be on the minimum 6" supply line per NFPA 24 (2022) Section 7.1.1.1. There is also no automatic drain in the bottom of a wet-barrel.
Reply