When sizing an elevated fire water storage tank for the minimum supply duration of a sprinkler system, should non-remote areas (areas closer to the tank) of the system be considered as well?
Since sprinklers closer to the tank would be under higher pressure, they would discharge more water than those in the remote area. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
12/19/2024 08:14:53 am
Officially the hydraulically most demanding area needs to be considered when sizing the water supply system to serve the building's sprinkler system(s).
Reply
Anthony
12/19/2024 08:15:15 am
Any sprinkler system water supply will be evaluated based on the DEMAND of the various hazards. The calculation will determine the minimum supply pressures and volumes required. Any extra pressure is "bonus" and will only aid in the system performance (below 175 psi).
Reply
Franck
12/19/2024 08:37:55 am
Not with NFPA where you size your water supply (pump capacity and tank volume) on the most remote area of the most demanding area in terms of hazard (could be EH gr 2 or based onna storage iccupancy demand).
Reply
Jesse
12/19/2024 08:44:30 am
The tank is sized based upon the automatic sprinkler demand. The demand calc is from the hydraulically remote area which is not necessarily the most physically remote area.
Reply
David Kendrick
12/19/2024 09:48:19 am
I enjoy reading questions and posts from subscribers to Meyerfire.
Reply
Jack G
12/19/2024 10:56:21 am
The tank is sized for the automatic sprinkler demand plus 5 % for the tank bottom ( sludge ) is how they are sized.