|
There's an existing system in a warehouse with a pump. It's a grid system with an 8" main and 1" 17k ESFR sprinklers.
The main is in a 3' wide inaccessible "hallway". They added office space that will require 15 heads. There's a 4" floater main nearby. Can I connect to the 4" main to feed the added sprinklers? What do I need to consider in doing so? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Dan Wilder
7/22/2026 06:56:18 am
Other than likely having to perform calcs, existing system survey, associated water supply and fire pump annual performance test, to prove your pipe sizing for the expansion (unless there is already an existing, more remote precedent for sizing), there shouldn't be much out of the norm to complete the work on the design.
Reply
Glenn Berger
7/22/2026 08:14:07 am
Yes you can connect to the existing 4 inch pipe to serve additional sprinklers.
Reply
Jesse
7/22/2026 08:33:35 am
I''d make sure first that you aren't exceeding system size limitations. If not, I'd proceed with designing and calcing the addition.
Reply
Jack G
7/22/2026 11:31:50 am
Single risers are limited to 52 k sq feet.
Reply
Pete H
7/23/2026 08:16:27 am
You can do it.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
