I have a contract that calls for concealed, extended coverage horizontal sidewalls in an area with a Turf Switchblade Acoustic Ceiling. The issue I'm running into is that the Tyco RFIII EC HSW has a maximum distance below the ceiling of 12", and the acoustic has a maximum dimension of 9.4" down from the ceiling.
Therefore, I won't have the 4" minimum distance between the deflector and the obstruction. Has anyone else encountered this type of issue? Has anyone found a concealed sidewall extended coverage that can be 18" below the ceiling? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
11/25/2025 07:49:47 am
They're not concealed, but based on this thread:
Reply
Colin B
11/25/2025 11:32:00 am
Thank you, I actually submitted those as an option with my RFI to the GC and Architect. They Specified concealed on the specs. Waiting to hear back. Thanks again.
Reply
Jesse
11/25/2025 08:18:13 am
In my humble opinion, HSW sprinklers are the most mis-used sprinklers out there. Their listings typically indicate usage beneath a smooth, level / flat ceiling or specify a slope they can be used with.
Reply
Colin B
11/25/2025 11:32:39 am
That's a great tool I was not yet aware of, Thanks!
Reply
Jack G
11/25/2025 11:04:57 am
A metal grid ceiling with tiles is usually considered a smooth ceiling per nfpa 13.
Reply
Colin B
11/25/2025 11:33:45 am
That's exactly the point I am at. I have an RFI sent in explaining the issue and am waiting for answers, just wanted to see if anyone had experience with this issue and knew an easier work around. Thank you for your reply!
Reply
Randy Rathert
11/25/2025 12:32:02 pm
That is one of the best conversations that i have followed on this site.
Reply
Mike
11/26/2025 10:33:35 am
Just from a Google image search, these don't even look like they qualify as acceptable construction type for sidewall sprinklers.
Reply