We have a condominium (3 story, 18 units), with an original 20-year-old Gast model 2LAF-12-M200X.
Complaint from the unit sharing an adjacent wall to the sprinkler room. The compressor repeatedly turns on and off only during the early morning hours, between 2 and 4 AM. We have monitored and seen nothing but normal activity during the day. Is this possible? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Chad
6/6/2025 08:11:07 am
Yes…. Temperatures affect the system pressure. It may be colder at that time.
Reply
David Kendrick
6/6/2025 08:22:54 am
Find the leak.
Reply
6/6/2025 08:25:21 am
The unit has been =identified to be 20 years old. When was the last time the pressure gauges/switch has been calibrated? I suggest to start from here before going to the next step.
Reply
6/6/2025 08:30:24 am
I would suggest doing the 3 year air leakage test outlined at NFPA 25 2023 in Chapter 13 at 13.4.5.2.9. This will help identify if you have a piping integrity issue. Then you can then look closer at a possible thermal effect issue or a compressor issue.
Reply
Jody Aycock
6/6/2025 08:37:15 am
It could be a few things, first make sure there’s not an air leak in the system, second if no air leak check the low air turn on psi for the compressor, it could be set too low, or your pressure switch on the compressor could be going bad.
Reply
Bill Harvey
6/6/2025 08:45:07 am
I agree with the other comments, if the compressor is functioning properly and no air leaks are identified I'd suggest adding a riser tank kit and an AMD from General Air Products. This won't fix any psi drop but it will reduce the number of times the compressor kicks in.
Reply
Dan Wilder
6/6/2025 08:55:13 am
As this is occurring during the coolest part of the night, you likely have a leak. Thermal expansion through the warming day keeps the pressure up but as things cool down, the pressure sensor trips.
Reply
Jesse
6/6/2025 09:23:56 am
My guess is there's a leak somewhere. The wramer day leading to some thermal expansion of the air in the system, but then not so much in the cooler evening.
Reply
6/6/2025 03:02:08 pm
There is an air pressure switch on the pump, which is what turns it on. The compressor will not turn on unless the air pressure has decreased.
Reply
Jeff Edick
6/8/2025 06:38:03 am
Sometimes the fastest way to find a leak (after the a/c fittings have been checked), is to schedule a system full trip test. Once the I.T. runs clear close it. Close the control valve also, close off any trim that’s running water too. Get a bright flashlight and begin tracing every pipe, looking for drips. I usually find several on older systems. Mark them, make a stock list, place a quote for repair work,or T&M it. Good luck.
Reply
Jack G
6/19/2025 03:43:02 pm
It looks like it’s a quarter hp 50 psi air compressor.