Hello, I am trying to figure out what commodity classification vinyl doors are.
I am designing a fire sprinkler system for a warehouse that stores doors and windows with the main materials being wood, glass, and vinyl. Doing a google search vinyl doors are typically made out of PVC (polyvinyl chloride). NFPA 13 - 2019 - Table A.20.4(b) lists the following: PVC (polyvinyl chloride) products, up to 20 percent plasticizer - Class III PVC (polyvinyl chloride) products, greater than 20 percent plasticizer - Group A Nonexpanded Table A.20.4.3 Examples of Class III Commodities has Furniture; wood (doors, windows, cabinets, etc.); So I'm thinking the next question that I need to ask is how much plasticizer is used in vinyl doors? I'm thinking it is less than 20% and use Class III. Any thoughts? Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Franck
10/24/2025 08:21:27 am
I’m afraid you will have to ask the manufacturer.
Reply
Glenn Berger
10/24/2025 08:32:05 am
You also need to know the configuration of the storage. The height of the facility vs. the height of storage and then the arrangement of storage.
Reply
Justin Reid
10/24/2025 08:56:11 am
Be sure to talk to the owner as well about what their future needs are. I understand wanting to limit to a lower classification but in my opinion you should design for future flexibility and design to the upper limits of your water supply.
Reply
Jesse
10/24/2025 10:20:13 am
I'd be really hesitant to call this a Class III without some really solid documentation. The plasticizer content can be up to 40%.
Reply
Jack G
10/24/2025 03:17:23 pm
Under 20%=0.2 class3
Reply