What is the NFPA Commodity Classification for fruit in plastic bins (for example, cherries, floor-stacked 20 ft. high)?
The bins are open on top with holes for drainage and are full of cherries. Do the bins make this Class I a Class IV or Group A plastic instead?
9 Comments
Pete H
2/27/2025 06:33:46 am
For me it depends on whether the fruits are dried or not. These do not look like dried fruits, and the plastic is not an empty container.
Reply
Jesse
2/27/2025 08:17:26 am
Packaging must alwats be considered and is more frequently driving the overall commodity class.
Reply
Pete H
2/27/2025 11:33:57 am
I was claiming expanded due to:
Reply
Glenn Berger
2/27/2025 08:30:32 am
Group A Plastic - The storage container has been typically the driver for the commodity type on my projects.
Reply
Jose Figueroa
2/27/2025 08:31:33 am
It depends! I recommend checking out this reading: https://www.nfpa.org/news-blogs-and-articles/blogs/2022/01/18/commodity-classifications-in-nfpa-13.
Reply
2/27/2025 08:52:12 am
This is a tough on. The container looks closer to a solid unit than gridded. Also failry substaintail. A case could be made for unexpanded, exposed Group A plastics. The sprinkler design would also cover the empties.
Reply
NK
2/27/2025 08:55:52 am
1) The protection criterias have changed in the newer editions of NFPA 13, but I don't think the commodity classifications themselves have changed much. NFPA 13, 2025 has improved definitions and organization for storage that I'd recommending reading. I'd start with these definitions:
Reply
Jack G
2/27/2025 02:08:30 pm
For me,changing wood crates for plastic ones , for storing fresh fruit , if the storage arrangement was solid pile ,to 20 ft—- maybe building height 30 ft , I d find that the density for a stable pile was. 1.1 gpm. / ft2.
Reply
Richard Stehr
2/27/2025 02:35:29 pm
Refer to 2021 International Fire Code Chapter 32 -Figure 3203.9(2).
Reply