Is there any relevant code or standard that restricts the use of flexible sprinkler armovers above hard ceilings?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
7/14/2026 06:13:20 am
There might be a local prohibition.
Reply
Dan Wilder
7/14/2026 07:44:38 am
Provided you are calculating the friction losses through them, no on the installation side from NFPA.
Reply
Glenn Berger
7/14/2026 08:39:43 am
Nothing in the codes that restricts the use of flex armovers as asked in the question.
Reply
Jonathan Griffin
7/14/2026 08:55:20 am
NFPA 13 (2022) :17.4.1.3.3* Flexible Sprinkler Hose Fittings, requires that the Flexible Hose assembly be mounted & supported by the OEM instructions. The Listed bracket must be attached to the ACT Ceiling grid (or Lay-in Ceiling grid) per OEM instructions to properly support the Flexible Hose assembly. A Gypsum hard Deck using 2' x 2' or 2' x 4' Lay-in sheet supports may allow the use of Flexible Hose to the sprinkler. Good luck!
Reply
andrew j koutsoftas
7/14/2026 10:48:43 am
Great point about the possible local prohibitions and/or modifications. An example is NYC Building Code modifying the hanging requirements for flex piping:
Reply
Jack G
7/14/2026 12:07:13 pm
Totally acceptable as long as you meet the attachment method and hardware listed in the flex drop literature.