Is there anything in the code that specifically talks about EV (Electric Vehicle) charging stations?
Anything that might say "If you are adding EV Stations in a garage the sprinkler system must be checked, upgraded or analyzed?" Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Glenn Berger
2/10/2025 08:13:01 am
The answer to your question is maybe! Once you add a "significant" change the occupancy may not be just a parking garage as defined in the IBC - Group S-2 to a potential Group S-1.
Reply
Meghan
2/10/2025 08:14:55 am
The Code hasn't caught up to this yet but you can request a re-evaluation of the sprinkler system based on NFPA 101:4.6.1.2 [2021]: Any requirements that are essential for the safety of building occupants and that are not specifically provided for by this Code shall be determined by the authority having jurisdiction.
Reply
Anthony
2/10/2025 10:06:22 am
I agree with Meghan here, code is lagging behind the technology. To be fair to the code authors it's VERY hard to remove a requirement once in place so mandating anything now based on current tech that may by obsolete in 2 years is a hard sell to most code bodies.
Reply
Chad
2/10/2025 11:55:33 am
Meghan is spot on, if you are an NFPA location. Its like the wild west right now. Some Local AHJs like San Francisco have adopted more stringent sprinkler requirements. They are extensive. Not sure if I agree with them or not, we dont have enough data but its not a bad idea.
Reply
Todd E Wyatt
2/10/2025 08:19:53 am
The scoping Code (e.g. IBC-2021) includes the following ELECTRIC VEHICLE CHARGING STATION (EVCS) references :
Reply
Ricardo Gonzales Jr
2/10/2025 08:40:24 am
I've been asking these questions sine the Surprise AZ incident. What I've decided to do is see what other jurisdictions are doing. I've paid attention to NYC since they have a dense population and NYC has mandated energy storage and the only places they can do that is within buildings people live in. What is FDNY doing? Another is California where I've scene plans where they treat EVs similar to Class A plastics for sprinklers. The idea is not to suppress the fire, Li-Ion will burn unless drowned, but to keep the fire from spreading.
Reply
Pete H
2/10/2025 09:30:54 am
Does your jurisdiction adopt NFPA 88A?
Reply
Franck
2/10/2025 12:19:34 pm
There is no actual regulation so far.
Reply
Jack G
2/10/2025 01:37:27 pm
No changes to codes yet, but will be forthcoming like initial reaction to solar panels on the roof of warehouses.
Reply
Jesse
2/10/2025 02:02:45 pm
Code really isn;t proactive, but reactive. Most of the code is derived from loss. Loss teaches us what doesn't work. And this is an area where the code hasn't caught up to the reality we live in quite yet.
Reply
The SFPE NJ chapter just had a presentation in regards to parking structures and what code changes are being updated to address these issues. The Presentation was by John Denhardt of the American Fire Sprinkler Association. Some big changes that he outlined are:
Reply
San
2/11/2025 01:15:46 am
Why not to apply Fixed Aerosol System for EV station. Its independent, reliable and activates based on flame temperature to quench fire.