Where in NFPA 13 or 30 does it say ESFR systems cannot protect ignitible liquids?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
6/5/2026 06:19:00 am
Most ignitable liquids would make this an Extra Hazard occupancy.
Reply
Brett
6/5/2026 06:38:33 am
NFPA 13:
Reply
JI
6/5/2026 08:10:21 am
NFPA 30 has the says the following in the annex in A16.1.1.
Reply
anthony
6/5/2026 01:35:28 pm
This answer says a lot with out saying it out right. Specifically with regards to the 3000 sqft remote area an EH system has compared to a nominal 1200 SQFT remote area for an ESFR system.
Chad
6/5/2026 08:08:05 am
What class ignitable liquids is key. do you have one in mind?
Reply
David Flavin
6/5/2026 08:40:25 am
NFPA 13 and NFPA 30 do not outright state that ESFR (Early Suppression Fast-Response) sprinkler systems cannot protect ignitible liquids, but they place significant limitations on their use
Reply
David Kendrick
6/5/2026 08:41:59 am
If this question is based on a change of occupancy and the desire to use an existing system wouldn’t it be appropriate to check the listing of the existing system sprinkler heads?
Reply