MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Code Basis for Replacement of 3/4" Branch Pipe?

4/25/2022

13 Comments

 
We have a project in an old building (historic city) that has 3/4-inch branch pipe in their sprinkler system. We've recommended, based on good practice, to change these out for minimum 1-inch due to the potential of obstructions, and that NFPA 13 has not recognized 3/4-inch branch pipe for over 50 years now.

The client is pushing back asking for a reference stating that 3/4-inch lines need to be replaced. I cannot find anything in NFPA standards which would "require" it.

Do you have any helpful references on this that would help educate the client here?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
4/25/2022 06:54:29 am

Nothing too concrete off the top of my head. You could claim that there's no listed steel fire sprinkler pipe currently less than 1" in diameter, and pursuant to NFPA 13 Chapter 6 (2016 edition and prior) the pipe has to be listed for fire protection, but I haven't double checked that there isn't any 3/4" pipe that's listed for fire protection, so maybe they could catch you with your pants down there.

You could also claim that if this is a hydraulically designed retrofit on a previously pipe schedule system, the current calculations and current water does not work for 3/4" branch piping, but I don't see your calcs and have no way to verify if that's true.

You could claim that you're trying to install flexheads for obstructions and adding the friction loss of the flexhead is why you need the 1" pipe sizing for your calculations.

You could claim if it is not a hydraulically designed retrofit that you're following current NFPA 13 rules regarding pipe schedules systems (It's around Chapter 23.7 in NFPA 13 2016, but you might have to look for the exact section) and the chart showing pipe sizing and heads that can be fed doesn't include 3/4" showing 3/4" is not an acceptable pipe size on current pipe schedule retrofits.

Hopefully someone else provides you with something more concrete.

Reply
Alex
4/25/2022 07:01:53 am

Hi,

I don’t believe there is a code section that states it needs to be replaced. Once touched, it needs to be brought up to 1” minimum but if you aren’t modifying it, then it can stay. Even if you are just replacing heads, I would replace the entire line. You touch it, you own it.

If you aren’t modifying it, I would still call for the piping to be internally inspected per NFPA 25 Chapter 14. Since the system is over 50 years, you are running an increased risk of build up over time. If foreign organic or inorganic material is found, I would replace the piping with a larger size contingent on hydraulic calculations.

Lastly, if the sprinklers are still original, they must either be replaced or a representative sample from the area must be tested (NFPA 25 5.3.1.1.1). This would in turn trigger replacing the ¾” lines.

Hope this helps!
Alex

Reply
Jesse link
4/25/2022 08:08:41 am

I'm with Alex here. I'm guessing this is an old pipe schedule system. If you're not modifying the lines, you could make the case for the 3/4" pipe to remain. But, if you're modifying it, it needs to be changed.

The case to replace it is strong. You may need to hydraulically calculate it to ensure any changes in the water supply don't render it inadequate.

Finally, depending upon who there property insurer is, the underwriter and Loss Control engineer may not allow 3/4" branch lines at all. I know of at least 3 insurers that don't allow it.

Reply
Matt C
4/25/2022 08:20:02 am

If you're going to hydraulically calculate the system at all, you can use 23.4.1.2. (in the 2013 ed.) which states ferrous piping shall be no less than 1".

Reply
Anthony C. Brown
4/25/2022 08:25:08 am

check with the AHJ. Some have code that will allow the last section of an existing system to remain 3/4" with the balance being replaced. Some AHJ will defer to their State Building Code on percentage of work being done for system replacement, i.e. If 50% (or some other benchmark amount) of a system is being replaced, then the entire system must be brought up to current code. Just be careful because I have seen several Municipalities use the base amount of the actual cost of construction, not the current cost of construction.

If all else fails then as has been suggested, use the 50 Year inspection and check the 3/4" pipe for sludge blockage. I bet you'll find it...

Reply
Craig Montoya
4/25/2022 08:53:36 am

I would have a conversation about the risks of doing a hydrostatic test at 200 PSI on the existing branch lines, and if that failed I would talk to the AHJ privately and tell them your concerns.

If this will mainly be a new system I think it is completely acceptable for an AHJ to use section of 1.4 on this project and make the owner replace these.

Reply
Joe Chadwick
4/25/2022 08:57:03 am

If this is part of a larger renovation, and the work is regulated by the Existing Building Code (IEBC), sprinklers may be required to comply with current code.
The Owner’s insurance carrier might have something to say.

Reply
David Kendrick
4/25/2022 09:38:57 am

Ask for the system internal inspection documentation. The smaller size pipe works until its filled with rust, corrosion or other debris.
Upon finding no documentation recommend a representative sample internal inspection.
Truly you touch it you own a certain responsibility.
The sprinkler business has a mantra taken from the real estate industry.

Documentation, documentation, documentation.

Personal opinion.

Reply
Karsten Smith link
4/25/2022 09:40:36 am

The first question I have is what is your scope of work for this project? Are you doing a TI, an addition, etc?

When submitting this to the AHJ will they require that you upgrade the pipe? If so, have the conversation with the AHJ before hand, discuss the project and they may provide you with local amendments/requirements that state you need to bring the
"affected area" or "entire system" up to current code.

Hope this helps.

Reply
John
4/25/2022 09:55:10 am

It appears that at the time of the original installation, three-quarter inch pipe was acceptable. Even though the current codes do not allow for this, the system in essence is grandfathered in. The owner isn’t obligated to upgrade the pipe sizes unless there is a serious physical reason to do so.

Please be mindful that unless a PE makes this type of recommendation, a fire protection contractor, cannot act in an engineering capacity. This may expose you to legal issues in the future

Reply
Dan Wilder
4/25/2022 11:08:50 am

Need some more info as to your scope and your scope language. If your scope includes changing the 3/4" lines to 1" due to hydraulic needs, then anything within your scope would need to be changed out (based on hydraulics proving the other pipe sizes all work). It would then fall onto a letter of recommendation that the areas outside your scope be changed (again, with a proof hydraulic calculation showing the pipe sizing all works to the end of the system),

If your scope includes changing sprinklers (with the same K-Factor in the case of a change out) but do not include a hazard change (see 29.4 below) you should be OK but not required to change pipe sizing.

When was the last internal inspection performed on the system? Since it's an old system, it probably looks like the day it was installed but it's a possible option. The other push may be that the AHJ has written in something requiring the change out for pipe schedule systems (I've seen this in older AHJ's to weed out the older systems).

NFPA 13-19'
19.3.2.3 - Pipe schedule is allowed based on the 4 criteria
27.5 - Allows Pipe Schedule systems if the original system was based on that design criteria
29.4.1 - Allows pipe schedules systems to be revamped.

Reply
Robert Hughes
4/25/2022 12:16:31 pm

Have the owner sign something stating they are dis-regarding your company's recommended standards and industry practice.

Reply
Eric Rieve
4/27/2022 12:12:42 pm

If the system was designed per pipe schedule, does the sprinkler riser have a backflow preventer that was retrofitted into the original riser arrangement? If so, how old is the backflow, and is there a hydraulic plate to show that the system was recalculated when it was installed?

We recently came across a similar situation where a backflow had been installed without a calc being performed, and this gave us an easy way to state that the tenant space needed to be recalculated which then found the 3/4" pipe to be lacking.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT