Valve Cabinet Clearance Is there any code which requires a minimum clearance for a valve cabinet. I typically say 36” or 1m (in Canada) as that is the typical clearance required in front of equipment. But I have been asked if there is any supporting reference for this specifically and I can’t find one for hose cabinets.
Just hose valves in a cabinet or where they are not to obstruct egress. Looking to see what others use and if they have any code reference. Along a similar thought - does anyone know if equipment access clearances can overlap, or do they need to be independent of each other? Can clearances overlap? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
4/3/2025 08:15:24 am
There needs to be operational clearance provided. I would hope that this type of "requirement" would not need to be put into writing.
Reply
Chad
4/3/2025 09:11:45 am
3' yes.
Reply
Chad
4/3/2025 09:15:15 am
Overlapping is fine, again assuming 3' clearance, IMO.... but not in the case of dedicated electrical space, see NFPA 70 110.26
Reply
Dan Wilder
4/3/2025 09:20:27 am
Typically, the Building/Fire code will prescribe distances.
Reply
Dave L.
4/3/2025 12:07:37 pm
I'm traveling at the moment and can't cross-check, but what about the 3 in. clearance required aroumd hose connection handles from NFPA #14"
Reply
Chad
4/3/2025 12:11:26 pm
I think you are referring to this? cant find 3ft/ 36 in elsewhere
Reply
chad
4/3/2025 12:12:26 pm
you mean inches yeah this:
Reply