Are stand-alone clean agent systems required to be monitored by a supervising station or constantly attended location?
I am reviewing plans for a small, remote equipment shed that is equipped with a clean agent suppression system. The building is remote enough and small enough that IBC wouldn't require a fire alarm or sprinkler system. The designer claims that it doesn't have to report out, but I think they're wrong. I think this would fall under the IBC 907.3 requirements for a dedicated function panel, which still requires supervision of the detectors at a "constantly attended location." Since the building isn't constantly attended, it would have to dial out to the central receiving station, not just to some guy's email. From what I've gathered, a full-blown FACP wouldn't be required, but a dedicated panel to dial out would be. What is your take on this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Chad
9/9/2024 08:03:35 am
You are spot on.
Reply
Glenn Berger
9/9/2024 08:10:47 am
Since the system is not required by code, then I see the differences in opinion on reporting alarms out. In my opinion, since a system is being provided, then remote notification shall happen.
Reply
Joe
9/9/2024 08:14:02 am
IFC 2021 edition section 904.3.5, would not require monitoring unless the building has a fire alarm system, but one would think they would go above the minimum level of care.
Reply
Sean H
9/9/2024 08:24:01 am
Here is what the IBC (2018 ed) states in section 904 covering Alternative Automatic Fire-Extinguishing Systems (like clean agents), that they may be basing the stance on:
Reply
Franck
9/9/2024 08:32:06 am
Not speaking of regulation, but common sense
Reply
Ricardo Gonzales Jr
9/9/2024 08:37:41 am
If it had only an elevator panel, no reporting necessary if there is no building fire alarm system. It is not there for Life Safety, only for equipment protection. Not required by code but by Owner request. I would not spend the effort to have it report as if there was an inadvertent alarm, you'd roll trucks to a site that has no occupants? As much as we'd like ALL types of fire alarms reported, I see it as a non-issue.
Reply
Todd E Wyatt
9/9/2024 08:39:50 am
The scoping Code (e.g. IBC-2021) determines WHERE fire protection systems shall be monitored.
Reply
Todd E Wyatt
9/9/2024 08:40:42 am
REFERENCES
Reply
Jack G
9/9/2024 09:40:05 am
I agree with Ricardo . Not life safety, no monitoring.