Where is the code section that states the numbers (calcs) on the supply side shall be greater than the numbers at the base of riser (system side)?
Does the code address this with a code section? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Peter Howard
8/28/2024 06:25:51 am
I don't know if it's code... but doesn't it have to work this way?
Reply
Anthony
8/28/2024 06:50:19 am
I think the following 2 code sections will suffice from NFPA 13-2016:
Reply
Dan Wilder
8/28/2024 08:00:32 am
Unless the building is downhill from the flow test location and/or goes through a pump, having a required pressure greater than the available pressure equates to the system not working.
Reply
Glenn Berger
8/28/2024 08:23:29 am
I agree with Dan. I had to review the question posed today. The Sprinkler System Designer is REQUIRED to ensure that the water supply must be able to deliver sufficient flow and pressure to support the proposed sprinkler system.
Reply
Joe C
8/28/2024 08:24:54 am
I had one system "base of riser" that was about 80' lower in elevation than the flow test hyrant on the hill above adding about 35psi. An of course it's an obvious result if you have a pump in-between the "source" and the "base of riser'.
Reply
Jesse
8/28/2024 08:50:55 am
Dan's on the right track here.
Reply
Jack G
8/28/2024 07:57:34 pm
Pretty sure you won’t find anything in the codes with that exact wording. NFPA 1142 shows how to evaluate the water supply..
Reply