Can a wafer check or grooved check valve be installed directly on a fire pump discharge flange?
I've found they affect the pump performance by 3 to 8 psi. When testing we found this true and moved it by a foot. The pump didn’t hit its curve and was fairly new. Shouldn’t NFPA 20 or manufacturers be aware of this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Mike Morey
10/24/2024 08:12:12 am
I've never heard of it being an issue, generally we put in full sized grooved swing checks for whatever it's worth. We install a LOT of fire pumps so I would think it would have come up by now. Though most of our real big pumps are Diesel so they have a relief valve which pushes the check out anyway.
Reply
Dan Wilder
10/24/2024 08:26:45 am
Acceptable as long as the pump is not required to have a pressure/circulation relief valve as that valve is to be installed first per 20-22' 4.20.3 (it's been in the standard since at least 2013).
Reply
Rob
10/24/2024 12:40:30 pm
I don't think it matters.... You are taking your pressure readings at the discharge flange prior to any check, regardless of its location.
Reply
Jack G
10/24/2024 04:28:01 pm
I was shown that a check with a split or rotating element , 6 inch, the check is 3 inches face to face or less ( tight pumproom )
Reply