I am working on a retrofit project where the owner wants to replace the existing electric baseboard heaters with electric cove heaters. Being a radiant heater, NFPA 13 clearly states that sprinklers within the high and intermediate temperature zones would need to be changed out to suit.
I am getting pushback from the design team, given the small size and low power (1KW) of the heaters. NFPA 13 seems petty cut and dry on this. Am I missing something? Anyone run into this before? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Pete H
4/15/2025 06:31:13 am
Sounds like you're right, but more information would be required.
Reply
Dan Wilder
4/15/2025 08:22:46 am
As these could be a longer, lower output system, there may be an argument that the discharge temp would not exceed a temp threshold. That would be an argument to lessen the restrictions, but I would still provide an intermediate temp sprinkler if it fell within the "pie shaped cylinder" space as described in the temp rating chart.
Reply
Jack G
4/15/2025 09:05:01 am
NFPA definitely has requirements for sprinkler head temperatures near difuser and heat sources and ceiling temperatures.
Reply
Leave a Reply. |