NFPA 13 Section 16.2.4 concerning protective coverings for sprinklers only references spray booths and mixing rooms.
I have a building that produces particulates in the air (a chip and tortilla factory). The concern is that we replace these sprinklers, and they will quickly need to be replaced again in a couple of years (96 total). I want to put on cellophane bags to protect them. The existing sprinklers are standard response. I plan to go to the AHJ for their approval, but I wanted to get the opinion of others who may have experienced something like this. Thank you in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
4/2/2026 07:36:17 am
We have used this method is this manner before as well however sourcing the cellophane bags at that thickness proved a little difficult (they are out there). Most are Polyethylene or other mix at that thickness.
Reply
Wes
4/2/2026 09:06:26 am
If procurement/bag type is an issue - would posting a very clear sign (placard?) saying what type of bag is allowed and where to buy replacements (QR code?), somewhere in the vicinity, be helpful?
Reply
Dan Wilder
4/2/2026 03:37:19 pm
My problem was ordering a specific bag, then once received it was incorrect.
Jesse
4/2/2026 08:18:24 am
I've seen / used this before for simiar facilities. Even though its not a spray room, the issue is the same as it relates to fugitive dust insulating the sprinkler.
Reply
Jack G
4/2/2026 08:32:34 am
See Meyer Fire 8/8/2024.
Reply
Glenn Berger
4/2/2026 08:35:37 am
Dan's and Jesse's responses have the proper information.
Reply
David Kendrick
4/2/2026 09:03:20 am
What type of scrutiny are you under being a food processing facility?
Reply
Jose R Figueroa
4/2/2026 11:02:14 am
I have seen this problem many times. NFPA 13 (Installation of Sprinkler Systems, including the 2022 edition section 16.2.4 on Protective Coverings) and related standards permit only cellophane bags ≤ 0.003 in. However, you should ensure it is true cellophane, which many people mistake for plastic. Additionally, I recommend replacing such bags at least monthly or as needed depending on residue buildup. Remember that this area is prone to explosion, so you should look for solutions to reduce the amount of flour in the environment.
Reply
Dave L.
4/2/2026 12:05:44 pm
True - Hear me now and believe me later; I was finally able to find true cellophane bags from a food packaging supply company.
Reply
Jose Figueroa
4/2/2026 03:26:44 pm
I'm concerned. The company should reduce flour dust in the enclosed area. Keep sprinklers clear of bags. The main risk is dust explosions. They need strict housekeeping with frequent floor sweeping, sometimes hourly. Protect electrical panels from dust. References include FM Global Data Sheet 7-75 and NFPA 61 for fire and explosion prevention.
Dave L.
4/10/2026 01:04:18 pm
Been thinking about this some more - I actually did a sprinkler T.I. for a similar facility that was down the road from us. I was not aware of particle accumulation. But this question resulted in my discovering NFPA 660, Standard for Combustible Dusts and Particulate Solids.
Reply