Looking for education on the cause of major sprinkler corrosion in a warehouse. A general warehouse with ESFR heads has a serious corrosion problem on approximately 600 sprinklers, with two inadvertent actuations occurring in the past 6 months. The image is of the worst corroded sprinkler. Others are more lightly corroded, each with a green hue. The actuated heads were sent to UL for evaluation as well as non-fused corroded heads. Tests indicated the heads functioned within normal range, with one head slightly delayed. The manufacturer confirmed the heads are not counterfeit. The conditions within the warehouse were unique for approximately 7 years, with very high internal temperatures occurring during the winter months, using once-through heating to ensure forklift exhaust CO ppm levels were kept low.
In addition to elevated temperatures, the warehouse received insect fogging applications as normal practice for stored seed and beans. Fogging has also occurred at other similar warehouses, and no problems have been observed at those locations. Corrosion is on approximately 15% of all sprinklers in the warehouse building area. Are there similar experiences with corrosion that is similar to the image? If so, what was determined to be the primary cause? Heat, chemical, or something else? All of the corroded sprinklers were replaced with new heads and NFPA guidance was observed for temperature selection near forced air heaters. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
7/29/2025 06:09:52 am
No similar experience:
Reply
Joseph Terranova
7/29/2025 08:09:23 am
It appears to be a chloride reaction with some dust accumulation. The pattern and coloration is similar to what is found in pool filtration rooms.
Reply
7/29/2025 08:09:28 am
With no obvious environmental concerns, I would check and see if there is electrical ground on the sprinkler system somewhere.
Reply
Glenn Berger
7/29/2025 08:20:48 am
Need to review the chemicals involved with the "insect fogging" application mentioned the write-up.
Reply
Jesse
7/29/2025 08:25:39 am
This is a fascinating one.
Reply
Franck
7/29/2025 08:29:52 am
Could it be related to the products stored in the warehouse ?
Reply
Chad
7/29/2025 08:42:08 am
I too wonder what the products are off gassing. Its most likely environmental, possibly whatever they fog it with.
Reply
Dan Wilder
7/29/2025 08:29:54 am
So brass & bronze will corrode green with both chemical and humidity factors. As you stated this is a seed and bean warehouse the chemical factor (typically chlorine) decreases dramatically, however with a high humidity level kept for most of these warehouses, this is more likely the cause. Due to the more uniform rusting on the pipe, the warm humid air rising within the structure will naturally condense on the pipe as shown.
Reply
Jack G
7/29/2025 08:49:45 am
I think Chris s explanation of electrical, ( I think the building is not grounded properly ) is the major problem, along with the chemical fogging, the ionization of corrosive particals.,
Reply
Jeff Ayers
7/29/2025 10:17:33 am
I had a garage in Baltimore with similar corrosion problems.
Reply
Greg
8/1/2025 08:23:14 am
Thank you for the insight. All responses have been very helpful and prompted further evaluation of makeup air entering the building.
Reply
Greg
8/15/2025 03:02:32 pm
Also, we verified that a fumigant containing phosphine products was not used in the warehouse's history. Phosphine containing fumigants have been known to cause metal corrosion.
Reply