|
Recently we encountered a system where the floor control valve assemblies (FCVAs) have pressure reducing valves (PRVs) that are due for their 5-year full-flow testing. Typically, we would conduct this through a hose valve downstream of the PRV (hooked up to the Drain Riser), but this arrangement does not allow for that. The only means of connecting the FCVA to the Drain Riser would be to shut down the floor, remove the grooved coupling & cap from this tee (clouded in the image below), and then hook up a connection to the Drain Riser. Then, another shutdown would be needed to replace the coupling & cap to return the system to its current configuration. When addressing Pressure Reducing Devices, NFPA 13, 2019, 16.9.8.5 states that “Means shall be provided downstream of all pressure reducing valves for flow tests at sprinkler system demand.”
However, according to NFPA 13 2019, 16.14.5.1, a “means shall be provided” for forward testing of the backflow preventer. This “means”, per 16.14.5.1.1, “shall be serviceable without requiring the owner to modify the system.” I am unable to find a similar reference that pertains to Pressure Reducing Devices. Is the capped tee considered “Means” to conduct the testing in this instance, despite requiring 2 shutdowns and “modifications” to the system? Or is a permanently installed valve required to be considered “Means” to conduct the testing? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
7/22/2025 08:10:51 am
This is very common on current installations and is, per the letter, a means to test the system. The 2022 Edition modifies this section to the following:
Reply
Glenn Berger
7/22/2025 08:17:47 am
You have a lot of items / issues showing up in the photo that are not making sense to me at this time.
Reply
BK
7/22/2025 08:29:39 am
This cap looks like a "means" to test. With the isolation valves and block valves on top, no need for a shut down or drain down to connect to the drain riser. I'm not saying its a perfect means.
Reply
Derek Wallis
7/22/2025 08:35:02 am
NFPA uses the term "means" loosely, allowing for the installer and the inspectors to comply with the standard in many different types of installations. I would agree with the installer in your example that "means to test the PRV's were provided. They left the grooved tee as a connection and in addition, they added the second butterfly valve (far more expensive than fixing a hose valve on each floor on the tee and eliminating the butterfly valve and all the associated alarm work) to accommodate for a quick drain and connection to the tee with the inspectors flow device and drain hose. Possibly not shown in the picture would be the connection outlet on the express drain. But even then, a quick disconnection of the 1-1/4" drain could suffice if you can flow the system demand through the 1-1/4" outlet.
Reply
Jesse
7/22/2025 11:33:48 am
Yeah agree with the term "means to test" used loosely and I would submit this meets that requirement. But like, Glenn I'm kinda wondering what I'm looking at there. Probably makes a lot more sense in person.
Reply
Chad
7/22/2025 01:04:17 pm
I hate it. But I agree
Reply
Anthony
7/22/2025 01:38:06 pm
Designed this many times, its very common and acceptable.
Reply
Casey Milhorn
7/23/2025 09:25:39 am
The capped tee is fine, even if not ideal. The possible bigger issue is lack of a properly sized test connection on the drain stack and/or possibly an improperly sized drain stack. You would refer to NFPA 14 (in my opinion), even for the zone assembly. NFPA 14 doesn't differentiate between a system PRV and a PRV hose valve.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
