|
When would we be permitted to remove a check valve from a zone control valve?
Like, what are the requirements for needing it one way or another? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
8/5/2026 07:16:03 am
Depending on your FDC setup, you could remove the check and still be in compliance with NFPA 13.
Reply
Dan Wilder
8/5/2026 08:54:04 am
Devil in the details, nicely quoted below gents for the Multistory...
Reply
Brett
8/5/2026 07:46:40 am
If it's a floor control assembly in a multi-story building then the check valve is required. See NFPA 13 (2019) section 16.9.11.1.
Reply
Aaron
8/5/2026 08:08:03 am
A check valve is required on a floor control assembly if it is connected to a standpipe system.
Reply
Glenn Berger
8/5/2026 08:24:20 am
Check valves should never be removed from zone control valves.
Reply
anthony
8/5/2026 09:45:50 am
"Like, what are the requirements for needing it one way or another?"
Reply
Pete H
8/5/2026 02:23:00 pm
Anytime you could remove the full control and check valve and unite two systems, then you can do it.
Reply
Jack G
8/6/2026 07:10:52 am
If feed is from a standpipe the zone control valve needs a check valve.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
