Hi everyone, I’m looking into the compatibility between UL-listed K-factors and European classification under UNI EN 12259-1.
Specifically, I’m reviewing a Viking upright sprinkler (presumed marked 5.6 gpm/√psi), with the typical UL listing and a 1/2” NPT thread. The orifice appears to be in the 10 mm nominal range. According to Table 3 of UNI EN 12259-1, a 10 mm nominal orifice corresponds to a K-factor of 57 ±3 l/min/√bar. However, UL 199 allows sprinklers to be classified as 5.6 even with some variation in orifice geometry, and the unit conversion from 5.6 US gpm/√psi gives approximately 80 l/min/√bar, which seems inconsistent with the European 10 mm / K57 classification. Have you encountered UL-listed 5.6 sprinklers that, due to actual geometry, fall within the K57 class under UNI EN? Are there known cases where K-factors "overlap" across standards? An excerpt from UNI EN 12259-1 Annex C below. Thanks for your insights — I'm trying to understand how this is approached in practice during technical evaluations or retrofitting in Europe. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
8/14/2025 06:09:41 am
https://www.refiregroup.com.au/product/sprinkler-k-factor-conversion-table/
Reply
Franck
8/14/2025 09:45:24 am
mm is the right measurement unit in Europe for thread.
Reply
Franck
8/14/2025 09:51:30 am
I had a look at https://www.refiregroup.com.au/product/sprinkler-k-factor-conversion-table/
Reply
Glenn Berger
8/14/2025 08:19:59 am
There are sprinkler manufacturers who have published data for the European (and other non-US) Market and the respective listings.
Reply
Franck
8/14/2025 09:40:57 am
The European standard is using what we could call an "abuse of language" and are mixing threads (the 10, 15 or 20 mm of your table) and orifice size, or making a direct relationship when this relationship is not always verified.
Reply
Pete H
8/14/2025 01:18:59 pm
Thank you Franck, cause I was not going to get there from maths alone.
Reply
James Art FPE
8/20/2025 12:35:17 pm
One sad thing was when the NFPA foolishly deleted the pintles required on fire sprinklers. Prior to that, if the orifice was other than the usual for the thread,
Reply