Calculate with SxL or Room Area in Small Rooms?

1/14/2022

7 Comments

 
In Section 19.4.1.3(3) of NFPA 13-2019 Edition, discusses that rooms or compartments 800 sqft or less (small rooms) should be calculated based on delivering 0.10 gpm/sqft over the room or the compartment by using the area of the room divided by the number of sprinklers in the room.

I believe I've overcalculated remote areas in the past.

My project now is an apartment building designed according to NFPA 13. Using residential type sprinklers with non-sprinklered combustible concealed spaces. According to Section 19.4.1.2 I need to calculate a minimum of eight sprinklers.

In the past I've calculated the eight sprinklers using the actual spacing based on the S x L rules with a 0.10 gpm/sqft density.

One room example - room dimension of 24 x 12 is 288 sqft. Two sprinklers spaced in a compartment 8'-0" off one wall and 6'-0" from adjacent wall. Using the S x L rule: 16' x 12' = 192 sqft x 0.10 gpm/sqft = 19.2 gpm each.

Or, according to Section 19.4.1.3 (3), would I divide the room size 288 sqft by 2 sprinklers, which is 144 sqft per sprinkler, regardless of the actual sprinkler distance from the walls? This second scenario would result in a 14.4 gpm required flow.

Or, was the code option (3) assuming the sprinklers are evenly centered within the compartment.

Thanks in advance for your input and clarification.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
1/14/2022 07:56:13 am

Here is a great explanation that should help you out.

https://nfsa.org/2020/12/01/the-nfpa-13-small-room-rule-frequently-asked-questions/

Reply
Alex
1/14/2022 08:17:46 am

Hi,

You can use the room area divided by the number of sprinklers. Note, that the sprinkler coverage cannot exceed the maximum protection area found in NFPA 13 (2022) Table 10.2.4.2.1(a). For instance, maximum coverage area is 225 ft2. If you room is 245ft2, you will need (2) sprinklers.

The link that Dan provided is a great help! Wish I had found that earlier when I was designing.

Alex

Reply
Danefre
1/14/2022 08:55:45 am

Just wanted to add that the NFSA article Dan linked was written in 2020, so while it does say that "small room rule" does not apply to residential sprinklers per section 10.2 (2019), you still calculate it as area/# of sprinklers per 19.4.1.3 (2019).

in the past, 2007-2013 editions, Chapter 11 would redirect you back to Chapter 8. In 2016, the area/# sprinklers verbiage was included in Chapter 11. You can see the difference in how 11.3.1.3 is written between the 2013 and 2016 editions.
Credit to Travis M. for explaining this.

Reply
Dan Wilder
1/14/2022 09:55:02 am

Nice...I glossed over the "residential" part of that because I don't equate small room (exceeding distance from walls) & residential sprinklers (basically EC spacing)...and the area/# of sprinklers approach typically is less than the minimum required for the sprinkler so I don't get to utilize it as much (what little residential I do anyway)

and yes, Travis has provided some pivotal advice in the past for me as well, so double credit for sure!

Reply
Jack G
1/14/2022 12:15:17 pm

You can find a formal interp that preceded the paragraph being added. It’s been in the book for quite a while.
Small room rule only applies to light hazard occupancies.

Reply
Casey Milhorn
1/14/2022 12:54:04 pm

This is one of the most common things that I find designers don't do correctly. You basically do two calcs when using residential sprinklers in a 13 system.
#1 is at a .05 density using the SxL method (but rounded up at 16x16, 18x18, etc per cut sheet) over the four hydraulically most demanding adjacent sprinklers. (Use manufacturers end head pressures).
#2 is at a .10 density using each compartments total sqft and area of heads is total sqft divided by number of heads in compartment. (use 7 psi end head pressure).
99% of the time you will find that the .05 calc is more demanding because of the SxL method and rounding up to 18x18, 20x20, etc... and of course the end head pressure.

Reply
Coorey Power
1/17/2022 05:32:02 am

This! I've been questioned on several residential under 13 projects Where I show the 0.05 calc is more demanding. My experience is for the most part when the room is under 800 sqft the 0.05 calc is the most demanding. A lot of reviewers seem to miss the part where you divide the area of the room over # of sprinklers.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT