I have a 3-story building with a vertical opening that connects all floors. The vertical opening communicates (no rated separations) with portions of floors 1 and 2.
When determining the sprinkler design area (1500 sq for light hazard); should sprinklers be calculated on all 3 levels since they are likely to activate from a fire at the bottom level? This would create some hydraulic challenges, right, since the heads at the bottom will see more pressure and flow much more water than the heads at the top? It would seem to be simpler to enclose the vertical opening so that all the heads would be at the same elevation (top), but it's an existing building where we are adding a sprinkler system. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder
10/21/2026 07:58:47 am
Not including any protection scheme requirements for the vertical opening, the calculation would be for each floor/system not a combination of multiple systems/floors.
Reply
Glenn Berger
10/21/2026 08:31:15 am
I would provide individual floor level designs including calculations. If the lowest level and the intermediate levels are designed completely identical, then you can avoid one providing the lowest level design.
Reply
Jesse
10/21/2026 08:34:50 am
Individual floor hydraulic remote areas should suffice
Reply
Pete D.
10/21/2026 09:15:53 am
Echoing others.
Reply
Brian
10/21/2026 11:36:25 am
It would seem to me that the purpose of draft curtains and draft stops is to prevent heat/smoke from traveling to floors above and fusing sprinkler heads. Not having this protection would allow heads to fuse on multiple floors, so it would seem that the heads around the opening on all levels should be included as a "remote area" and calculated.
Reply
Mark Harris
10/21/2026 04:03:20 pm
Not enough detail but may need water curtain sprinklers 6-0 on center around the opening. But to the original question agree with the comments that you only calc one level at a time. If there is a water curtain requirement may need to include those sprinklers in calc for the first and second floor calculations (but agree with Glenn that if they are similar, you would use the intermediate level calc for the lower level as well).
Reply
Streeter
10/21/2026 04:48:14 pm
This would only come up to me as a consideration if every floor area that communicated was less than 1500sf. And even then the sprinklers above the fire (whether on floor 1 or 2) or floor 3 if is is a 3 story atrium, would activate first to put out the fire.
Reply
Jack G
10/21/2026 08:46:00 pm
Under the Latest IBC (2024) and NFPA 13, a 3 story vertical opening connecting all floors without a fire separation is treated as an atrium ( section 404) or a communicating 2 story opening requiring an automatic sprinkler system thru out plus closely spaced sprinklers and draft curtains if relying on non rated open shaft alternatives.
Reply
Jack G
10/21/2026 08:57:14 pm
I believe the AHJ would want water curtain sprinkler added for each of communicating draft stops to the most remote market floor calc. ( length of mra box divided by spacing of sprinklers times however many communicating floors without the 1-2 hour fire barriers. )
Reply