Calculate (%) Safety Factor for Sprinkler Systems?

4/1/2019

13 Comments

 
For hydraulic safety factors (such as in fire sprinkler systems), determining whether a 5 psi safety factor is met in a design is easy. The Available Pressure must be greater than Required Pressure + 5 PSI.

However, for percentage safety factors such as 5% or 10%, is the percentage calculated based on the Required Pressure or Available Pressure? 

As an example, if we have a system that requires 80 psi and the available city pressure of 88 psi, a 10% safety factor on the required pressure would be 80 psi x 10% = 8 psi safety required. In this case the minimum is met. However, a 10% safety factor on the available pressure is 88 psi x 10% = 8.8 psi safety required. In this case, the safety factor is not met.

This is an extreme example, but I'm curious what others would use when looking at determining safety factors.

Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
13 Comments
Wayne Ammons
4/1/2019 07:34:39 am

NFPA 13 does not mandate a safety margin for hydraulic calculations. However, it is a good idea to maintain some amount of safety margin to account for fluctuations in water supply.

Many companies and jurisdictions require a safety margin in psi and some require a safety margin percentage. In my experience working with jurisdictions all across the country, determining what this percentage is calculated from varies. Most often the percentage is of available city static pressure, sometimes it is of system demand pressure.

You will want to contact the company, AHJ, or municipality that is requiring the safety margin and confirm exactly how to calculate the safety margin.

Reply
Scott Walter McBride
4/1/2019 10:10:40 am

I would agree with Mr. Ammons. At the end of the day it is up to the AHJ of what the requirement is and how it is to be calculated.

Not to mention that there are safety factors that are built in to hydraulic calculations to begin with, but don't argue that with the AHJ. You will lose.

Reply
Andrew Valente
12/1/2025 01:54:18 pm

It is not up to the AHJ to determine the safety margin because the AHJ is only allowed to enforce the written code, and since NFPA 13 does not have anything written about a safety margin the AHJ is not permitted to enforce one. That would be like saying the AHJ can enforce a safety margin on exit stair and exit door width.

The safety margin for sprinklers is built into the requirements. For sprinkler they are built into the hydraulic calculations in the form of design area, or as for ESFR the number of sprinklers to calculated. This is evident in the exceptional performance of fire sprinklers, in which 90-something percent of fires are controlled with the activation of one or two sprinklers. While most of this performance in in light and ordinary hazard systems, (the number of sprinklers in offices, residential and retail stores exhibit an incredibly reliable performance). As well as most failures are due to a shut valve and not inadequate design.

J Mcelvaney
4/1/2019 10:14:26 am

The City of Phoenix, AZ has the following design safety factor

507.4.2 Design safety factor.
The water flow test results shall be adjusted as noted in Sections 508.1.4.5.3 and 508.1.4.5.4 to account for seasonal and daily flow calculations in the water supply system.

507.4.3 Static pressure over 90 psi.
When the static pressure is over 90 pounds (621 kPa) per square inch (psi) the maximum design static pressure will be 80 psi (552 kPa) regardless of the actual test pressure. The slope of the original design curve shall be used even though the design pressure is reduced to 80 psi (552 kPa).

507.4.4 Static pressure less than or equal to 90 psi.
When the recorded static pressure is less than or equal to 90 psi (621 kPa), the system design shall include a minimum 10 psi (69 kPa) safety factor between the system flow and pressure demand and the available water supply.

Reply
Mike
4/1/2019 10:15:38 am

CBC requires 10% reduction of the available water supply flow test to be used. I use a minimum of 10% below that.

Most of the time it's just making, riser, riser nipples or starter pieces one diameter larger. This is usually very economical compared to the risk.

If you're doing a retrofit with many unknowns you can use a larger factor or larger starters for unanticipated offsets.

A really common oversight i have seen in when using flexible drops, the correct equivalent pipe length isn't used for the length of the drop and maximum number of turns.

I've also seen clowns put in a 4“ backflow in a 6“ supply to save a few $$$. This leaves no room for future changes.

Reply
Jake Zlomie link
4/1/2019 10:16:47 am

From my research, there is not a specific safety factor that is required for these systems, unless there is a specific ordinance adopted by a community or you are utilizing design criteria for a specialized industry. For example, the department of energy requires a 10% or 10 psi, whichever is greater based upon their DOE-1066 standard.

Some communities that also provide flow rates for your initial design, may reduce that by 10% to accommodate for a safety factor. When I researched this, many of those on the design end did not feel it was necessary based upon the safety factors already built into NFPA 13 design criteria as well as hydraulic calculations.

From an AHJ perspective, I think that the safety factor makes sense based upon when the flow was actually tested, fluctuations in the system, degradation and modification of the water supply, as well if the system was existing pipe schedule and then being hydraulically calculated.

Without an amendment or ordinance on the books however, the AHJ does not have a specific thread to pull in the event they find the calculations to be less than desirable. You could in theory submit calculations with a 0.3 safety factor otherwise.

Reply
RJ
4/1/2019 10:21:49 am

I have always used the following when asked for a percentage:

Safety factor psi divided by Available psi. For example:

Safety factor = 14.8 psi Available = 59.3 psi

14.8 ÷ 59.3% = 24.95

Reply
Dennis Clark
4/1/2019 11:16:39 am

The City of Sioux Falls requires the following:

The public water distribution system is subject to pressure fluctuation due to various seasonal and usage demands. Water pressure fluctuation is reported to be up to 10 psi annually as documented by the City of Sioux Falls Public Works Department.

A minimum pressure safety factor of 10 psi shall be added to all hydraulically calculated sprinkler pressure demands.

Reply
PETE
4/1/2019 11:22:18 am

It looks like I am late to the thread, but echoing some others above: a 10% safety factor would be on the demand pressure. That is, 110% of the calculated demand pressure would have to be less than or equal to the residual pressure in the water supply at the demand flow.

Reply
Alan A. Luce, NICET IV SET link
4/3/2019 05:06:33 am

10 psig equired in Georgia against the available water supply. However, remember to calculate available suction pressure on the inlet flange of a fire pump based upon 150% of the rated flow at 65% available boost per NFPA 20. This suctionnpressure must not be lower than 25 psig to protect the city water supply from potential backflow conditions.

Reply
Jessica Lutz
4/3/2019 10:04:54 am

In LA County and some other areas in SoCal, they require a 10% reduction of the pressure available at the supply.
In the Boston area, most specifications require a 10 psi safety between the demand and available pressures.

Reply
Chris Nelson
10/16/2026 08:29:23 am

Longshot due to age of comment, but as the AHJ in Boston, can you direct me to where you have found 10 psi? I am more inclined to enforce the 10% rather than 10 psi

Reply
Chris Nelson
10/27/2026 08:38:50 am

Just putting this for record, we have chosen the 10% safety factor rather than 10 psi here in boston officially,




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT