I have a campus housing situation with a few thousand reliable 3.9k heads that are no longer made, on 16x16 spacing, requiring 17 gpm and 19 psi per the cut sheet.
We are looking to replace these with 4.2k sprinklers, same 16x16 spacing, is 16 gpm and 14.5 psi per the cut sheet. Question is, I know the 4.2K falls just over the allowed 5% deviation, but these 4.2k sprinklers are more "efficient", so would they require running new hydraulic calcs to verify, or would it be safe to swap out as is? Thank you in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
5/20/2026 06:07:49 am
In terms of buereaucracy/AHJ's: Yeah, you still need to recalc. You changed the flow characteristics of the system.
Reply
anthony
5/20/2026 12:09:05 pm
As usual I agree with Pete here. Engage the AHJ early here you MIGHT get an allowance for a head swap. Worst case if you need to recalculate the system as other have said and you're back to the place you started form.
Reply
5/20/2026 07:54:42 am
This is a two fold question....
Reply
Jesse
5/20/2026 08:34:49 am
Anytime we're changing the hydraulic characteristics of a system I'd want to calculate it to prove the larger origifice sprinkler will work,
Reply
Glenn Berger
5/20/2026 08:40:34 am
As others have said; recalculation required. With the higher k-factor, at the same minimum pressure, you will required more water for the system and therefore a greater pressure at the source to meet the new demand.
Reply
Dave L.
5/20/2026 11:20:43 am
See also NFPA #13 (2025) 30.3.6 -
Reply
Dave L.
5/20/2026 11:22:00 am
(I guess I'm not sure exactly what kind of sprinklers you are replacing)
Reply
Jack G
5/20/2026 07:13:21 pm
So are we talking about a 2 or 4 head residential sprinkler calculation ?
Reply
James Art, FPE
5/22/2026 12:26:44 pm
"Next Larger K Factor" NFPA 25 says this:
Reply