C-Factor for a 55-Year Old System with Debris?

10/22/2024

11 Comments

 
Hydraulic Upgrade to old wet and dry systems and determine "C" factors to be used. Question:

We plan to upgrade a fire sprinkler system from a Pipe Schedule Ordinary Hazard system with k-5.6 standard response heads to 0.25/2000 sqft with k-8 sprinklers, what "C" factor should be used?

The system is 55 years old
and has a good water supply that would easily work for a new system using a C=120; however, debris has built up in the pipe, and if we were to do a hydro-pneumatic flush, the roughness would be much worse than that of new pipe.

The AHJ has no answers other than to do what we feel is best, and the insurance company just wants to see the density increased and "proven" to work at 0.25/2000. Furthermore, there are 2 dry systems that are 55
years old, and they want these upgraded, too. Even if we add a pump, it's just going to slam the sludge to the end of the lines and plug up any new heads that are installed.

Do you have any thoughts?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
10/22/2024 06:52:09 am

There's no outright code requirement for "Old black steel that just had debris flushed out and is now significantly rougher inside." so I can see why the AHJ told you to do what you think is best. Because technically, you could submit this as a C=120 on the wet system (the dry systems would be C of 100).

Is the density increase because of storage/commodity or is that the AHJ's thought to how to handle the impediments within the pipe?

You sound like you want safety for piece of mind, so flush the system, and if you want, arbitrarily calculate it for C of 100 on the wet, and C of 90 on the dry, while hitting the AHJ's .25/2000 density (and .25/2600 on the dry). But you're already in a grey area and it sounds like the client isn't looking to replace the old piping/system. If the potential debris based impairments cause relevant issues, let it come up on the annual inspection (obstruction investigation as per chapter 14 of NFPA 25 2017 Edition), and resolve it accordingly. But right now you're just proving the water in the system for the design works.

Reply
Alan Kavanaugh
10/23/2024 10:30:49 am

Howdy Folks,

C Factors are based on pipe materials, type of materials and interior finish of pipe. Assuming brand new pipe installed or after flush why would you give an Alarm System (Wet System) a higher C factor than a Dry system?

Reply
Pete H
10/23/2024 10:55:02 am

Because a wet system always has a higher C factor than a dry system.

Check Table 23.4.4.8.1 (NFPA 13 2016 edition).

Black steel (wet systems including deluge) C = 120

Black steel (dry systems including preaction) C = 100.

A lower C factor means rougher pipe / increased friction loss.

Dry systems have rougher pipe coefficients because the lack of constantly being filled with water actually causes more impairments or unexpected materials within the pipe to develop and cause greater friction loss.

So if the OP wants to feel safer, as they outlined, they calculate their systems with lower C factors than required just based on the expected additional friction loss from the age of the pipe developing a greater amount of impairments.

Pete H
10/23/2024 10:57:58 am

And to be fair, not always, a nitrogen based dry system can attain a C factor of 120 in newer editions of NFPA 13.

Alan Kavanaugh
10/23/2024 11:38:54 am

Thanks Pete for that clarification. Still doesn't make sense to me based on new installs? As you described roughness is based on the type of pipe not the sprinkler system factors? Interesting.

Jesse
10/22/2024 08:16:06 am

I think Pete is on the right track, and I also am curious as to the driver for the density increase.

The AHJ saying "do what you feel best" is akin to them saying we dond't want this albatros around our collective necks. I'm concerend about the debris and sludge in the system.

I got to wondering what I would do if this project came through my office and I'm not too sure I'd want my stamp on it... J

Reply
Glenn Berger
10/22/2024 08:31:11 am

I experienced this situation in the past and I wanted an invasive piping inspection conducted.

In the end, the entire piping system was replaced because of the build-up discovered in the piping system.

This is a designer beware scenario. Your question does indicate that debris was discovered in the pipe . This situation must be remediated.

Reply
Jesse
10/22/2024 09:02:13 am

Yeah Glenn that's kind of where I was going in my comment.

We had a hotel remodel. The hotel was changed to low income housing. Understand that the number of calls I was involved in as a FF / Medic to this particular place was incredible. It was a rat hole, and tdhat's being nice. We were modifying existing AS and adding a standpidpe system and fire pump. We recommended replacing all existing piping and they wouldn't.

Until the hydro test.....

Reply
Franck
10/22/2024 09:19:36 am

I would recommend at least to replace the entire dry sprinkler system.
I had an experience in the past where we tested a quite old dry pipe system from the ITC, and the water pushed all the debris and sediment to the far end where it blocked the sprinkler orifice with absolutely no water coming out.
This is definitely not what you want on a fire event.
And we had to replace the entire system.

For the wet pipe system, if sprinklers are pendent, you will probably need to replace all of them as sediment will have accumulated over time on the orifices.
A careful flushing is necessary and you will have to flush all dead ends… This might be a painful operation and with an unknown result.
If I was the AHJ, I would definitely recommend to replace it all.
It is 55 years old, it has made its time !

Reply
franck
10/22/2024 09:24:24 am

In addition, when you will restore the entire system and remove sediment and scale, corrosion will certainly starts with new fresh water and you will experience leakage and other maintenance issues.
Not to speak about the ability of your system to sustain pressure on the mid-ling term with no degradation on the piping system.

I would not be the one Responsible for accepting this situation.

Reply
Jack G
10/22/2024 11:36:45 am

There is a formula in the haven Williams/ equations where you can measure the flow and pressure between 2 points and calculate the c- factor.
Since you were flushing the system, you could have done this in several locations, come up with a c factor.
In the 60 s Kemper used to figure the age of the system was the drop in the c factor. 55 years = 65 c factor. I like testing and calculate c s for the branches and cross mains and supply mains better. Use those c factors in your hydraulic program.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT