I have a curved roof structure over a waterpark that has a top of steel of 37'-6" on the ends and 59'-8" at the peak.
Portions of the roof are also retractable, leaving little to no steel to hang from. In these areas where the roof retracts, joist girders are 16'-8" apart east to west, and we have purlins running north to south that are over 18' apart. We were looking at potentially using EC heads, but have a pretty good roof pitch, or using standard heads and spacing couplings between girders; however, hangers would be 16ft apart. How might you attack this, given the wide spans of the joist girders in one direction and purlins in the other? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
3/27/2026 07:45:57 am
Just spit balling this morning...
Reply
Zack Hinson
3/27/2026 08:18:16 am
There are a few exceptions to break the 15'-0 hanger spacing rule in FM 2-0 that you could consider. You would need to discuss it with the AHJ and get their approval of course. I have only ever used it once.
Reply
Jesse
3/27/2026 09:09:56 am
My first reaction is that I'm glad this your project, and not my project.
Reply
Rob
3/27/2026 03:23:01 pm
Standard heads ...... and trapeze everything.
Reply
Jack G
3/28/2026 11:29:59 am
For tent structures at Great Adventure, an FM global insured,
Reply
Rocket
3/29/2026 11:55:49 am
Start by classifying the commodity.