We have a project for a Aircraft Hangar Group II. We will be designing the foam system based on Inline balance pressure proportioning design under NFPA 16 Annex material.
The protected area has been divided into 3 zones. We are using an 8" Alarm check valve with a closed-head sprinkler for each zone. So the fire line is fully pressurized with water. What proportioner should I be using? Is it an inline balance pressure proportioner or a wide range / variable range proportioner better to get the 3% concentration when foam discharge at the nozzle? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
12/27/2024 08:24:47 am
Your question does not mention how is the foam being delivered to the proportioner. You do need to work with the foam supplier and get their details on their approved system configuration.
Reply
Dan Wilder
12/27/2024 09:02:01 am
The proportioner is a part of the system as a whole from the foam storage to the discharge and there are several factors to be considered from supply curves to balancing and testing.
Reply
Shawn R. Block
12/27/2024 10:26:47 am
I agree with Glenn and Dan. It is more important than ever to be working with a foam manufacturer. Especially if selecting the Closed-Head Foam-Water option for a Group II Aircraft Hangar. Many manufactures have discontinued (or are phasing out) AFFF and have switched to Synthetic Fluorine Free Foam (SFFF) listed for firefighting use for Class B fires including hydrocarbon fuels. The difference using SFFF is not a one for one comparison (or replacement) with AFFF. The manufacturer will guide you on which form proportioner would be appropriate for your system. Furthermore, they should be able to provide you with information on sprinklers (discharge devices) listed with their foam concentrate and the design density for that sprinkler. Keep in mind it may be higher than 0.16 GPM/SF than what NFPA 16/ NFPA 409 prescribes.
Reply
Jack G
12/27/2024 11:51:11 am
A few years back we did a similar installation at McGuire AFB.
Reply
Jesse
12/27/2024 12:23:03 pm
Another in agreement with Glenn and Dan. Really need to have the foam supplier involved in this.
Reply
Gérald
12/27/2024 02:23:12 pm
I would recommand a Firedos or a Firemiks or a Firepacks system according to FM approved With listed spk heads and SFFF emulsifier adéquate for the hangar height.
Reply
José Figueroa
12/27/2024 04:06:24 pm
I agree with many of the comments above. It’s important to involve the foam supplier in the decision-making process and to use <FM> materials. Given your requirement for a consistent 3% foam concentration at the nozzle across different zones, the “Inline Balance Pressure Proportioner” would generally be the more suitable option. However, this is mainly an educated guess.