Automist Systems for 1- and 2-Family Units?

10/13/2026

6 Comments

 
Moderator note: two submissions, similar themes:

Does anyone have experience with Automist systems?

The manufacturer/UL listing is for 1- and 2-family units.

My apprehension is
that the installation recommendation is to be at 4 ft AFF, and with tenants not knowing what it is, they may put furniture in front of it. An architect is trying to get me to use it, as they have used it for other jurisdictions, but I am not sure.

Hello, I am an AHJ who has been contacted about Automist systems for ADUs in lieu of a NFPA 13D system.

Has anyone used this before?

My Fire Marshal and I agree that the 4 ft mounting height AFF, with the chance of occupants putting furniture in front of them, as well as the 10-head max per pump, seem like disadvantages, especially when the expectation is that protection be extended when other units are renovated. (Our jurisidiction permits only the ADU be protected initially).

Was wondering how other FPEs thought of directed residential water mist systems despite them being UL listed for 1-2 family homes.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Brett
10/13/2026 07:28:29 am

If you're an NFSA member they have a Plumis webinar scheduled for 10/28. I am not familiar with the technology beyond having had Plumis show off their technology at an NFSA meeting previously.

I don't work for NFSA or Plumis. It just seems like Plumis may be the system that OP is referring to and, if not, is at least a similar system.

Reply
Anthony
10/13/2026 07:46:16 am

You can always provide restricted allowance.

"System type is approved with the provision that no instillation shall be less than 6ft AFF"

Also make the submission party work for the alternate. It's the submission's responsibility to alleviate your concerns and prove, with engineering certainty they have provided an equal alternative.

ALWAYS remember an AMMR provides an equivalent degree of safety to the code intent - not less because someone submitted paper work.

Reply
Brian Gerdwagen
10/13/2026 10:20:24 am

This puts too much burden on the occupant to be useful. If these were listed to be installed at the ceiling on the center of the space, maybe. This is a terrible idea as it stands. Your homeowner's insurance will not pay out if you had a chair in from of the device, the last owner painted over the plates, a renter put a bookshelf in front, etc. Their website has this installed above a kitchen counter below a cabinet.

This is a solution looking for a problem, not good protection.

Reply
Jack G
10/13/2026 11:56:08 am

I ve had experience with mist systems on ships. I like them on the boats, limited water supply, high pressure mist which saturates the fire and puts water spray into the atmosphere. NFPA 750. Extinguishes Fire by rapid cooling , displacing oxygen through water vapor expansion - steam expands up to 1700 times— and blocking radiant heat. I ve also had experience with Steam sprinkler systems on ships, and asphalt saturators inlenolium plants. ( from a high pressure steam system on boats/ plants) )
( FM global 7-101)
Expense was astronomical in my opinion.
I believe in the economics and safety data sheets for NFPA fire sprinkler systems. 13 d life safety is the best economics for homes, I d use concealers. I also would recommend dry sidewalls in the garage since fires have an affinity to start there. ( garage fires account for 2% of fires, 93% are in 1-2 family townhomes/ residential buildings, more than 50% spread beyond the garages, into the living spaces—- according to NFPA.
MAYBE, an automist system here and the kitchen range and mech equipment areas?

Reply
Jack G
10/13/2026 12:04:08 pm

Automist uses expensive sensors and alarm systems and wiring. Another “ expense “ to consider. I ve employed optical type detectors on industrial projects using mist.

Reply
Yusuf link
10/14/2026 07:33:12 am

Hi everyone, I'm Yusuf, co-founder of Plumis, the manufacturer of Automist. I thought I could provide some context and address a few of the concerns raised here.

Automist has now been installed in over 17,000 properties worldwide, with a long history of use in the UK. We have spent many years developing, installing and refining the technology, and our design practices reflect that experience, supported by independent fire testing and real-world activations.

On mounting height and obstructions
The approximately 4 ft mounting height is deliberate. Automist uses infrared sensing to locate the fire and directs water mist towards it. Positioning the nozzle lower allows mist to be introduced below the hot upper smoke layer, where it can be drawn into the fire plume rather than evaporating before reaching the fire.

We recognise that furniture obstruction is an important consideration, which is why our design guidance places considerable emphasis on spray head positioning.

We typically locate heads alongside light switches or other permanent architectural features, where occupants are less likely to place furniture. A clearance zone is required around each head, and in larger rooms multiple heads provide overlapping coverage from different positions. The system selects the head with the best view of the fire.

There is also a distinction between water mist and conventional sprinklers. Water mist doesn't depend entirely on directly wetting burning surfaces. The fire's convective plume entrains the fine droplets, helping mist circulate around partial obstructions and cool the fire gases.

These principles were also tested. The UL 2167A programme specifically included fire tests with obstructions between the spray heads and the fire, and Automist met the required performance criteria.

On the 10-head limit and future renovations
The 10-head limit applies to an individual pump and controller set, not to the entire property.

Automist is modular. Additional heads can be added to an existing system within its listed limits, or another independent pump and controller can be installed when additional coverage is required. This makes it possible to extend protection as a property is renovated, subject to the applicable listing, design limits and occupancy requirements.

Each operating pump discharges approximately 2.37 GPM. Water supply demand is therefore based on the number of pumps required to operate simultaneously, rather than the total number of heads installed.

On cost and complexity
I agree that traditional NFPA 13D sprinklers are often a very economical solution, particularly where the existing water supply is adequate. We don't see Automist as a replacement for conventional sprinklers, but rather as another tool in the fire protection contractor's toolbox.

There are specific situations where it can offer real advantages.
For homes with vaulted ceilings, exposed beams or complex architectural features, wall-mounted spray heads can avoid some of the challenges of conventional ceiling-mounted sprinklers, while preserving the architectural design.

For ADUs and residential retrofits, the largest expense is sometimes not the sprinkler system itself, but the infrastructure needed to support it. Water meter upgrades, new service connections, utility tap fees and trenching can add tens of thousands of dollars to a project. Automist's low water demand means it can often operate from the existing domestic supply, avoiding much of that expense.

Modular and prefabricated homes are another good example. The spray heads, dry hoses and wiring can be installed in the factory, reducing the amount of work required on site.

On evidence and equivalency
I agree with Anthony's point that an alternative means and methods request must demonstrate an equivalent level of safety, not simply rely on paperwork.

Automist is UL 2167A listed for one- and two-family dwellings under the NFPA 750 framework. UL Solutions has confirmed the alignment between the residential life-safety objectives of NFPA 750 and NFPA 13D, and Jensen Hughes has completed an independent engineering equivalency assessment.
We have assembled the certification, technical reports, fire testing and installation guidance specifically to help AHJs evaluate the system:

https://automist.us/faq/automist-ahj-submission/

We also have documented six real residential activations in which Automist stopped fires from spreading, including incidents where the occupants were asleep or not present to intervene:

https://automist.us/wp-content/uploads/2026/07/Automist-Activation-Stories-US-Customer-Version-VC1.pdf

Finally, thank you to Brett for mentioning the NFSA webinar.
My co-founder, William Makant, will be presenting at the NFSA's October MEME webinar on Wednesday, October 28, from 12:30 to 1:30 pm Eastern. He'll explain the principles of water mist, electronically controlled nozzles and how we're applying the technology in residential fire protection.

It's an opportunity

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT