Are Standpipes Required for Open Stairs?

4/22/2025

7 Comments

 
I have a new build design where standpipes are required due to height. An area of the building is lower than the height requirement. This area has a partial floor above another that looks over an open emergency planning room area. There are two open stairs at either end. They appear to be the only stairs.

I view these as required interior exit stairs, and since I have never found an exemption to areas of the building below the height requiring standpipes, I've included hose connections.

The Architect wants them removed because they are open stairs.

Are standpipes allowed to be omitted for open stairs in the portions below the required heights for a standpipe?

Any thoughts or input are appreciated.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Chad
4/22/2025 11:52:28 am

If the building height is lower than the requirement, why would you see it as being necessary?

Unless this is a very large building and the standpipe is wet (and remote from any exterior doors), there is no value to having it there, IMO.

Reply
Pete H
4/22/2025 02:06:05 pm

If you don't see an exception, there might not be.

At this point, maybe reach out to the relevant AHJ?

If they will accept the different height as a reason to exempt the standpipe, exempt away.

If not, tell the architect that your concern is a system that can be approved by the AHJ.

Reply
Wes
4/22/2025 03:05:22 pm

Usually the term is for hose valves to be located at "required exit stairs" or similar verbiage in the IBC/IFC and NFPA 14. If an open stair is a convenience stair, meaning its supplemental and not a required exit, then it wouldn't require a standpipe hose connection. See IFC 905.4 for an example where it says "required interior exit stairways."

That's assuming that you'd still meet travel distance requirements to a hose valve from all the portions of the building.

Reply
Casey Milhorn
4/22/2025 05:46:53 pm

I've never seen an exemption for required exit stairs, only for convenience stairs. I would DEFINITELY involve the responding fire department on this and let them be a part of this decision if they are left out. I don't think I would want to be a first responder showing up to a location where I had deficient numbers of hose connections. In similar situations, we have installed a concealed standpipe adjacent to the stairs in a chase, with hose valve cabinets. Make sure to provide rated cabinets if in a rated chase or wall.

Reply
Glenn Berger
4/23/2025 08:39:00 am

Based on your review that you have found no exceptions to the standpipe requirement, then it is required.

The comment does not indicate the number of floors in this building, the floor areas, or the distance from the exterior, or anything else that may lead to a detailed review.

The use of only open stairs needs to be investigated as how these are code compliant and might lead to a differing response.

Reply
Jack G
4/23/2025 07:57:36 pm

Wes and Glenn have hit it.
First of all if the architect/ engineer require it then it’s required as they have included on the code sheet.
Since the open stairs are not in a required fire rated enclosure, I m assuming the A&E are calling them convenience stairs.
So let’s call them that. Stairs for say 2 floors like an office and occupants can physically interact with each other. ( assumption)
So do these 2 floors in the “ different” part of the building, are they connected to the real egress stairs or not? ( how do they exit the building)
If not that might be a problem . Let’s say on the convenience stairs portion of the building , one floor must exit thru the other, and then the fire tower thru a connected fire rated hallway to the rated egress stairs. That’s a problem. If a corridor connects the floor and the rated stair tower, addition hose valves would be required on each side of the fire doors.
The open stairs may also be in the egress and require valves also.
The A&E should have an egress drawing for the building and each floor. So an AHJ &. A&E review should occur reviewing the plan documents as I think somehow those floors are in that portion of the buildings egress.( speculation, needed more information)



Reply
Julio Escobar
6/30/2025 03:07:47 pm

Gentlemen: If the stair exit is considered and Emergency Exit and is required for building height, a hose valve is required to approx. 150 ft pathway & 130 FT hose radius, if there is another stair far away in the building more than 150 ft path-way these additional stairway will required standpipe or if there are additional stairwell and overpass the pathway distance a FHC will be required to cover the hose radius, but these installation shall be fire rated including the wet standpipe riser protected. If these stair ways are not enclosure and open at each floor, the standpipe risers need to be rated protection and the opening will required a water curtain protections.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT