Do I need a separate 6" fire line to a building sprinkler system, and a second water line for all other uses?
This is for an NFPA 13 system. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Chad
6/17/2025 07:26:25 am
Depends on the water company/department plus the sections below (2019 NFPA 13) As long as it calcs out, it could be shared. The domestic demand is required to be accounted for. Same for 13R and D, although D uses a fixed 5GPM domestic demand
Reply
Anthony
6/17/2025 08:16:21 am
Depends on the municipality. In some areas its common to have separate lines so the water authority can shut off your domestic water for non payment and not have your building burn down.
Reply
Jesse
6/17/2025 08:17:17 am
Yep you can, but there are some pitfalls. I recently had a project in Houston where there was an existing fire line and RPZ. Everything calc'd and was though fine until we were told that the domestic demand, or non-fire water was also coming off of that same fire line. So we had to add additional backflow preventers to the risers in each building which killed our calcs.
Reply
Glenn Berger
6/17/2025 08:26:49 am
It depends on your locality and their regulations. Also check with the Owner's Parties having interest on the project as they may have additional requirements.
Reply
Dan Wilder
6/17/2025 09:06:40 am
Not a requirement and others have given some good feedback above.
Reply
Jack G
6/17/2025 09:35:31 am
It’s probably for most public utilities that separate dedicated lines are required so if you don’t pay your water bill ( and they shut you down) your building still has fire protection. This is prevalent for water companies in my jurisdiction.
Reply
Mark
6/17/2025 01:42:30 pm
I am an AHJ for a local municipality in Illinois, and the municipality requires a combination main into the fire protection/meter room which then is teed to the separate mains. The plumbing inspectors have explained to me that this is a State requirement in the Plumbing Code to avoid cross-contamination of the municipal water distribution system and dead-end mains.