MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Are Climbing Walls a Sprinkler Obstruction?

7/12/2022

9 Comments

 
We have a climbing gym that's in construction. See the image below.

The architect is calling this out as an assembly space, so we have light hazard upright protection up at the roof only.

The fire marshal walked the building and has concerns that the climbing walls create obstructions.
Picture
Are the climbing walls a construction concern? Any other input here?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/12/2022 06:51:39 am

Seems like a floor mounted obstruction if it goes up high enough. I'd say as long as you're following Table 8.6.5.2.2 (NFPA 13 2016 Edition) you're okay. So as long as there are more than 18" vertical distance between the deflector and the top of the climbing walls, I wouldn't worry about your horizontal distance to the wall or your spacing.

Reply
Alex
7/12/2022 07:43:21 am

Hi,

When you say construction concern, are you asking if the wall creates an obstruction to sprinklers? If that is the case, just confirm measurements with Table 8.6.5.1.2 and Table 8.6.5.2.2.

When the wall protrudes outwards, is it greater than 4 feet? That would be the only area where I can see the code official pushing back. Personally, I think only ceiling coverage is required either way.

Thanks,
Alex

Reply
schulman
7/12/2022 08:05:33 am

anything that leaves a large enough area of the floor without water during a fire is an obstruction

Reply
Jesse
7/12/2022 08:11:03 am

We just did a very large project like this and dealt with this same issue.

First, assembly doesn't drive design criteria. Occupancy hazard class does.

In my case, the climbing walls sloped to create a semi-inverted climbing experience. My concern was it creating a shielded area below. We discussed it at length with our AHJ and determined the slope wasn't sufficient to trap heat to activate a sprinkler. So we designed to OH2 (0.20 / 1,500 w/ 250 hose) and spaced sprinklers about5 feet from the perimeter of the climbing walls.

Reply
Franck
7/12/2022 08:17:08 am

Not a technical point of view (it has been highlighted above), but a practical point of view : is the climbing wall combustible? Is there something at the bottom of the wall combustible? If the answer is no to both questions, then what is the problem? Your ceiling sprinklers would cover a “no hazard” area…

Reply
Dan Wilder
7/12/2022 08:27:12 am

Most times, just the vertical portions aren't an issue.

The inclines/overhangs greater than 4' have been the issues in the past along. We have had to drop lines beneath some catwalk structure then had to add a sprinkler or sprinklers. We used concealed sprinklers and have used both bright chrome or brass along painting a large yellow circle with a warning around the sprinkler location.

Reply
Glenn Berger
7/12/2022 08:42:11 am

Climbing walls are a vertical obstruction as defined by NFPA 13. My experience is that if there is sufficient clear space on the top of the climbing wall, then sprinkler protection does not require modifications.

Reply
Greg
7/19/2022 08:54:09 am

In one of my experiences with climbing walls, the position of the wall against a interior hallway wall created a void space. The space was used for storage of ropes and climbing gear. It was large enough to enter through a small hatch door and included a light switch and light. The interior of the climbing wall was a resin. A sprinkler was extended into the space and I believe we included a wall recessed valve to isolate. The wall valve was labeled. This was a work-around achieved following a preliminary occupancy walk-through when the space was discovered.

Also, I spy with my little eye .... in your picture what appears to be a HVLS Fan. If it is, do you remember the rules for those and sprinkler activation, etc. etc. ?

Reply
Tracy
9/10/2024 02:45:58 pm

What about the crash pads? Does anyone know if the crash pads push the combustibility load out of light hazard or if they required to have a fire resistance rating?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT