MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Sprinkler Distance from Bathroom Heat Lamp?

11/28/2025

3 Comments

 
Under NFPA 13, how far away should an intermediate temperature sprinkler be from a two-bulb, 500-watt bathroom heat lamp?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Does Manual Standpipe 5-Year Need Fire Dept.?

11/27/2025

4 Comments

 
In a 3-story building with 3 standpipes, one of which is a combination standpipe/riser, and the standpipes are manual wet, with 50 psi.

On a 5-year test, how do I flow 1000 gpm (no pump) at 100 psi?

Do I involve the fire department?

The old hydraulic plates showed 70-50 at 260 flow. Three years later, they are showing 50-40 at 320 flow.

So I cannot pass this, even though the water supply has diminished.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

4 Comments

Tie Duct Detectors to Sprinkler Monitoring Panel?

11/26/2025

6 Comments

 
We are completing a buildout for a spec suite; the shell warehouse building was just constructed and has a fire sprinkler supervising panel.

The fire department is saying we have to tie the duct detector into the fire alarm panel. This building does not have fire alarm, only sprinkler monitoring.

Are they correct in saying we have to tie in the duct detector?

Thank you!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

6 Comments

Concealed EC Sidewall at 18" Below Ceiling?

11/25/2025

8 Comments

 
I have a contract that calls for concealed, extended coverage horizontal sidewalls in an area with a Turf Switchblade Acoustic Ceiling. The issue I'm running into is that the Tyco RFIII EC HSW has a maximum distance below the ceiling of 12", and the acoustic has a maximum dimension of 9.4" down from the ceiling.

Therefore, I won't have the 4" minimum distance between the deflector and the obstruction.

Has anyone else encountered this type of issue?

Has anyone found a concealed sidewall extended coverage that can be 18" below the ceiling?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Keep NPSHₐ > NPSHᵣ At All Times Pump Running?

11/24/2025

6 Comments

 
According to NFPA 20, for any pump installation, the NPSH supplied must be at least equal to the NPSH required for the operating conditions specified.

So does the NPSHₐ need to be continuously
maintained at or above the NPSHᵣ during pump operation?

During the operation of the fire pump, the liquid level of the fire water tank will keep dropping, which may lead to a situation where the NPSHₐ is lower than the NPSHᵣ (unless the fire water tank is built at a very high elevation).

​Is this situation permitted?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Dry Sidewall Sprinkler That Throws 23-ft?

11/21/2025

10 Comments

 
We are designing a project that has a porch area (approximately 88-ft long x 23-ft deep) at grade with occupied enclosed building space above it (the building overhangs the porch by 23-ft).

To avoid a costly dry-pipe system for this area, the CM is looking to serve this area from dry sidewalls connected to the buildings automatic wet sprinkler system.

Is anyone aware of any dry sidewall heads (exposed or concealed) for this application that can throw 23-ft?

​The building will have a fire pump so the extra pressure would not be an issue. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Model Adjacent Spaces for Elev. Pressurization?

11/20/2025

2 Comments

 
I am modeling the elevator pressurization system in CONTAM to demonstrate compliance with SBC 201 (IBC-based) requirements.

Normally, we use simplified spreadsheets, but code enforcement now requires performance verification through simulation.

In a model where the elevator shaft is adjacent to a protected service lobby, shell and core area, and a loading bay, is it sufficient to demonstrate pressure differentials only along the egress path (shaft → lobby → stair), or should other adjacent but enclosed spaces also be included?

What method do you recommend for extracting and presenting results—direct export from simulation (as in ASHRAE Applications, Fig. 21 Ch. 54) or summarized plots similar to Fig. 11.13 in the Handbook of Smoke Control Engineering, 2nd Ed.?

Lastly, when modeling the shaft, should it be defined as a flow path with cross-sectional area and perimeter replicated across all floors, except the top floor?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Standpipe for Scissor Stair Need 500 or 750 gpm?

11/19/2025

4 Comments

 
For scissor stairs having 2 separate standpipe risers (one of them is a combined sprinkler and standpipe system) running 12 floors, how do we size the pump flow rate required?

Can we argue that we can use
a 500GPM pump since the Risers are in close proximity to each other and are within one stairwell, or should we use a 750GPM pump following the NFPA 14 sizing of 500GPM plus 250 GPM per additional riser?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Data for False Activation in Pre-Action Systems?

11/18/2025

7 Comments

 
Could anyone point me to statistics to show how likely a single interlock pre-action sprinkler system is to spuriously or falsely activate?

A client is concerned about possible water damage in a
high-voltage switchroom that could damage their gear​ and cause a lengthy business interruption.

I have tried examining NFIRS data, but its format makes it difficult to analyze without a background in relational databases. I would like to explain the relative risk to the client in terms of 'it's a 1 in 100,000-year event you are concerned about' or whatever the stats point to.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Most-Used Fire Alarm Monitoring Setup Today?

11/17/2025

6 Comments

 
How do you coordinate what dialing out method with the client/telecom group, etc.?

A new fire alarm system, let's say a college building, for example, what do you typically see?

Does the college have its own monitoring station? Do you dial out signals via cellular or internet, or both?

Do dial-out signals go to both the college monitoring station (say, a life safety office) and a central monitoring station?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

When are Multiple-Row Racks Solid-Shelves?

11/14/2025

2 Comments

 
Can someone explain NFPA 13 20.5.3.1.3 for Multiple Row Racks?

Unless the requirements of 20.5.3.1.3.1 or 20.5.3.1.3.2 are met, multiple-row racks without solid shelves shall be considered racks with solid shelves.

Section 20.5.3.1.3.1 Multiple-row racks without solid shelves shall be considered open racks where both transverse and longitudinal flue spaces are provided at maximum 5 ft (1.5 m) intervals. 20.5.3.1.3.2 Multiple-row racks without solid shelves shall be considered open racks where transverse flue spaces are provided at maximum 5 ft (1.5 m) intervals and the rack depth does not exceed 20 ft (6.1 m) between aisles that are a minimum width of 3.5 ft (1.1 m).

Does this mean you have to have a 6-inch flue space on all 4 sides of each pallet load every 5ft within the rack, OR a 6-inch transverse flue space every 5ft, but the rack cannot be deeper than 20ft?

​Is it one or the other, and do you see one more often than the other?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Estimating Sprinkler Pressure Loss from Friction?

11/13/2025

5 Comments

 
I have a quick question about estimating the pressure requirements for an automatic wet sprinkler system during the initial design phase.

Qm = d X (Area per Sprinkler)
   = (0.15) X (130sqft)
   = 19.5 gpm

Estimated Total Flow (ETF) = Qm X N X F plus hose demand
   = (19.5 gpm) X (12 sprinklers) X (1.30 for spray pattern overage) + 250 gpm (Outside Hose Stream)
   = 554.2 gpm

Minimum pressure needed for the system.
   = (19.5gpm/5.6K)
   = 12.13 psi for the most demanding sprinkler + another 20-35 psi for potential friction loss throughout the reference.

The total estimated pressure needed would be 47.13 psi, not factoring in elevation change. The 20-35 psi for potential friction loss is an engineering judgement based on experience.

What is the recommended potential friction loss for an initial design phase, and where would it be referenced at?

I need to reference the source of recommended potential friction loss for the project. SFPE, NFPA or etc?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Always Sprinkler Under 24"+ ESFR Obstructions?

11/12/2025

3 Comments

 
Question in relation to ESFR sprinklers. Per NFPA 13 2016 Section 8.12.5 - obstructions 12" to 24" wide, the sprinkler must be 2 feet away.

There is no specific code for obstructions larger than 24"; does this mean these obstructions would always require coverage beneath?

I ask because I have a 36" cable tray - if it's centered between two branch lines, can I apply the code to half the obstruction?

​In this case, the head would be further than 2' from 18" of the obstruction on both sides.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Protect Small 'Bumpouts' for Classroom Partition?

11/11/2025

7 Comments

 
I have a project where there are small bumpouts on either side of a room that are sized just big enough to store an accordion ceiling partition when not in use. The partition divides a bigger classroom into two smaller classrooms when used.

Do I need to somehow have sprinkler coverage in the bumpouts?

The small areas are only exposed when the partition is deployed, which results in two even smaller spaces on each side of the partition. NFPA 13 Section 9.2.9.1 seems like one possible code section to allow an omission.

What are your thoughts on this allowance?

​Seems challenging to incorporate sprinkler protection in those small areas and not very practical for the low fire hazard they present.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Ceiling vs. In-Rack for Automated Warehouse?

11/10/2025

9 Comments

 
In an automated warehouse, is it feasible to replace the in-rack sprinklers with ceiling sprinklers on the upper racking levels?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Dry Pendent Sprinkler for Outside Dust Collector?

11/7/2025

6 Comments

 
I have a project involving an outdoor dust collector. My firm specified a dry-pipe sprinkler system for it.

The contractor asked if an antifreeze loop would be acceptable as a substitute, and we said no, as the AHJ does not want to deal with the maintenance side of an antifreeze loop long term.

The contractor states that the head connection in the collector is pendent instead of upright, and they can't go with the dry system because of trapped water concerns. I think a dry pendant sprinkler would work as it's allowed (even required if an upright is not used) by FM Data Sheet 2.0.

​Anyone install a dry pendent in a dust collector, and have any drainage issues or had to add a drum drip or other means of drainage to make the system work long term?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Standpipe Connection On Floor Without Door?

11/6/2025

10 Comments

 
I have a hotel building that requires a standpipe in each of the two staircases. One of the stair shafts has a door to the outside at grade level, but there is no door to the first level inside. The lowest level with an interior door is the second floor, which has its own hose connection.

It doesn't make sense to provide a hose connection at the ground floor, but is there a code basis to support this?

Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Thank You to Top October 2025 Contributors!

11/5/2025

0 Comments

 
Thanks for fueling a stronger community this season! Here are the top contributors for October! 
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
0 Comments

Use Bench-Testing for Pressure Reducing FHVs?

11/5/2025

4 Comments

 
Does anyone have experience with bench testing pressure-reducing FHV's?

We have horizontal corridors in a hospital, and having a fire hose and flow noise/water in certain areas is not an option.

NFPA 25 2020 Edition, A.13.5.2.2 allows bench testing (i.e.
 remove the FHV, take it outside to conduct the 5-year test).

Has anyone performed this? What is the procedure, and did the AHJ find it acceptable?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

What Ceiling Height with Warehouse Ridge Vent?

11/4/2025

9 Comments

 
Good morning, I'm designing sprinklers for a Class III warehouse. The warehouse has a ridge vent that's currently enclosed on the side walls.

What ceiling height should be considered for the design: the average ceiling height or the height of the center of the ridge vent?

The lower part of the ridge vent is 39.66 ft, and the upper part is 41.5 ft.

If I consider 39.6 ft as the height, I could work with a 25.2 kPa sprinkler at 25 psi, but if I consider 41.5 ft, I should consider a pressure of 40 psi, and the fire pump would change.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Each Townhouse Have Its Own NFPA 13D System?

11/3/2025

17 Comments

 
My coworker and I are disagreeing about townhomes.

Can each townhouse (3 total) have its own NFPA 13D system?

Or do they need to have one total system?

Each townhouse has a 1-hr separation in the form of UL U347. I cannot find anything that says they
can't each have their own, but he is saying he can't find anything to say they can, to which I have always said if it doesn't say no, then it's usually allowed.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT