MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Swap Smoke Alarms with System Smoke or A/Vs?

11/29/2024

2 Comments

 
I have an R-2 convent with existing 120v smokes in the sleeping areas and they are installing a new FACP including low frequency notification in the sleeping areas.

I’ve read the commentary for IBC 907.5.2.3.3.

Would you say based on this section that they would need to either replace the existing 120’s and install system smoke detectors, or change the existing 120’s to a combo audio/visual model?

I'm trying to determine if the intent behind this is that the existing 120v smoke alarms now would also be required to activate visible signaling as well. 

​Appreciate your input!

Moderator: Link Directly to IBC 2021 907.5.2.3.3


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Are Draped Fabrics Obstructed Construction?

11/28/2024

5 Comments

 
We have an atrium on our project, and due to some changes in the interior design, fabrics (half circles drops) were added as shown in the attached pictures.

This has an impact on my sprinkler coverage and obstruction.

Can those fabrics (450mm depth) be considered as obstructed construction under NFPA 13 Section 11.2.4.1.2 (2) – NFPA 13 (2019 or 2022)?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
5 Comments

Water Storage Tank Recirculation Requirements?

11/27/2024

3 Comments

 
I am working on a fire pump station project.

As the water tank ( 2 x 50,000 gal) is dedicated to the fire pumps only, a possible stagnation is expected, and hence, a recirculation pump for the tanks will be the best solution. I saw in many forums or searches that an 8-hour refill needs to be incorporated for the pump sizing, however, I couldn't find anything solid on NFPA 22 documents regarding recirculation.

​Can someone direct me to the NFPA reference for the recirculation requirements?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Why Change of No NFPA 13R for > 30-ft Top Floor?

11/26/2024

5 Comments

 
Why is there a drastic change for limiting an NFPA 13R sprinkler system from a four-story, maximum 60 feet height above grade plane in IBC 2018 to the maximum of the top floor being only 30 feet above fire department access in IBC 2021?

Here, we have many townhomes (R-3 group) that could easily comply with the 2018 edition of the IBC, but they will exceed the top floor 30-foot limit of the 2021 edition of IBC.

Also, the 2024 IBC tries to fix the drastic change by providing an exception for Group R-2 buildings by raising the top floor height limit from 30 ft to 45 ft. That's great and all, but townhouses are still considered R-3 buildings and do not qualify for the exception.

How would you proceed for a townhome with a top floor over 30 feet above fire department access?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Duct Detector in Supply (72) or Return (IMC) Duct?

11/25/2024

11 Comments

 
NFPA 72 (2016) Section 17.7.5.3 says a duct smoke detector is required in the supply air duct; on the other hand, the IMC (2020) Section 606.2.1 says a duct smoke detector is required in the return air duct.

Which should I follow?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

20-Year Sprinkler Testing for Renovated Building?

11/22/2024

10 Comments

 
Per 5.3.1.1.1.3, NFPA 25, 2014 Edition, states that sprinklers manufactured using fast-response elements that have been in service for 20 years shall be replaced or representative samples shall be tested and then retested at 10-year intervals."

What is the common practice for doing a
20-year sprinkler test sample on a multistory office building built 20 years ago that has undergone numerous tenant renovations, where sprinklers have been replaced and added throughout the years?

My thoughts would be that maybe the common areas would have original sprinklers, but what would be the best way to approach this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Smoke Purge for DoD Buildings Over 2 Stories?

11/21/2024

6 Comments

 
UFC 3-600-01 (with change 6, 2021), Section 4-29.2.1 requires a manually activated smoke exhaust system for Limited-Access Structures three stories or more in height, with 6 air changes per hour throughout the entire building.

NFPA 101 (2024), Section 11.7.3.1.2 and 11.7.3.2 outlines that if there are
no unobstructed operable openings, openable from both the exterior and interior of the building, the building is defined as a Limited-Access Structure.

Most DoD buildings have security requirements that do not permit operable windows, especially not from the exterior
or the interior. Therefore, most DoD structures over two stories in height would require these post-fire smoke purge systems; however, I have not seen them actually being implemented on projects.

Is there an alternative code path I am missing, or have you designed and installed these systems in UFC projects?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Where is Detection for a 5-Level Deluge System?

11/20/2024

4 Comments

 
For a deluge system with pilot sprinkler detectors in a column (5 levels), where is the pilot line required?

​At what levels do we need detection?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

How to Construct In-Rack Barrier for FM Global?

11/19/2024

2 Comments

 
In-Rack Horizontal Barriers according to FM Global Data Sheet.

Were can I find any details about how to place the horizontal barrier using FM Global Data Sheet 8-9 Scheme 8-9a?

In NFPA 13
, there is a figure (NFPA 13-2016 Figure 17.1.2.9.4.2(A) ) showing this,​ but I can´t find any such figure in the Data Sheet.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Sprinkler Criteria for Exterior Opening Protection?

11/18/2024

7 Comments

 
What is the design criteria for exterior openings protected by a water curtain in IBC 2021?

Section 705.8.2 (protected openings in exterior walls) says that opening protection is not required when the building is sprinklered in accordance with NFPA 13 and when the exterior openings are protected by a water curtain approved for that use.

"Water curtain" is not defined in the IBC or NFPA 13.

NFPA 13 (2019 edition) gives design approach requirements for water curtains in Section 19.4.3, but none apply to protecting openings in exterior walls.

What is the intention of the IBC here? Window sprinklers? Exposure protection sprinklers?

​Is there a different NFPA standard that covers the design of this water curtain?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Any Listed Stainless Steel Pipe, Hangers, Rod, & Fasteners?

11/15/2024

3 Comments

 
Is there any listed stainless steel fire sprinkler pipe, hangers, rod, or fasteners?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Are Sprinklers Allowed Directly onto 3-inch Pipe?

11/14/2024

10 Comments

 
I designed an in-rack system, and due to the available pressure, I needed 3" diameter pipe feeding the sprinklers.

The fitter, who I respect as a knowledgeable person, thought that sprinklers were not permitted to be installed directly off of pipe greater than 2-1/2". He was not able to provide a code reference.

​I searched NFPA 13 and came up with nothing to confirm or deny what he was saying. I'm wondering if anyone else is familiar with this limitation. Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Sprinkler Required at Top of Roof Access Shaft?

11/13/2024

4 Comments

 
Is sprinkler protection required at the top of a roof access shaft?

This would be located in a stairwell that is otherwise protected. We'll say the shaft is 2'x3' in plan view, and 5' from the stair ceiling to the rooftop hatch. This is in a steel structure building, with concrete block stair shaft walls finished with gypsum. A permanently attached ladder is provided.

​Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

5-Year Required for 1.5" Class II PRVs in NFPA 25?

11/12/2024

3 Comments

 
In NFPA 25 (2013), Table 13.1.1.2 directs us to the Testing requirements for Pressure-Reducing "Hose connections," with a frequency of 5 years.

Does this apply solely to 2.5-inch PRV Hose Valve outlets, or does it include the 1.5-inch PRV Hose Valve outlets on Class II (and Class III) systems as well?

Can't seem to find specifics on that. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Does IBC Ch. 9 Apply to 2 Buildings on Same Lot?

11/11/2024

8 Comments

 
Section 503.1.2 of the IBC seems pretty clear that the intention that two buildings on the same lot can be considered 1 building if the comply with the height and aggregate areas comply with the height/area limitations.

However, does that also apply to Chapter 9 requirements?

For example, if Building A requires a sprinkler system based on its size/occupancy, does Building B need one even if its size and occupancy wouldn't require it?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

NFPA 72 Limits for Beam Detector Environment?

11/8/2024

3 Comments

 
Does NFPA 72 (or other standards) have any limit for the environment in which the beam detector is allowed to be installed?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Does NFPA 30 Chapter 16 Apply if Under MAQ?

11/7/2024

9 Comments

 
I don’t often dabble in NFPA 30, so I have some specific questions regarding the protection of flammable and combustible liquids that I am having issues finding straight answers to.

I have a sprinklered general-purpose warehouse that stores flammable liquids in container sizes less than or equal to those indicated in NFPA 30 (2021) Table 12.8.1. The total quantities (MAQs) of these containers are also less than those shown in Table 9.6.1.

NFPA 30 (2021) Section 12.8.1 indicates that “The liquid-container combinations listed in Table 12.8.1 shall be permitted to be stored in a general-purpose warehouse without quantity limits if protected in accordance with Chapter 16."

An older version of NFPA 30 (2015) Section 12.8.1(1) indicates that if “the applicable provisions of NFPA 13 for 20ft high storage of Class IV commodities based on the storage configuration of the liquids” is used for protecting these containers, no additional protection criteria is required barring the storage arrangements are in line with the rest of the Section 12.8.

My questions are as follows (per NFPA 13 -2021):

1. If combustible liquids are stored in amounts under the MAQs stated in Section 9.6.1 (and IFC) are the additional requirements of Section 16 (NFPA 30) required, no matter what?

2. If combustible liquids are stored in container sizes less than or equal to those set forth in Table 12.8.1 (NFPA 30), are the requirements of Section 16 still required?

3. Will the storage of these commodities within liquid storage cabinets negate the requirements set forth by Section 16?

The bones of the matter is that I am having a hard time finding a section directly indicating that the requirements of Section 16 are not required. Most if not all sections I can find only indicate that Section 16 is to be used when something is stated.

​Thank you all ahead of time. As always this forum has always been a wealth of information.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Extend Sprinkler How Far Beyond a Service Area?

11/6/2024

4 Comments

 
I am trying to find how far to provide sprinkler coverage past the edge of the above-ceiling mechanical service area.

There will be mechanical units and duct work in this area, the floor is covered with 3/4" fire resistive plywood over metal studs. I would also like to know where to reference this in NFPA 13 for future use.

​I attached the drawings for reference the hatched area is the service area. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
4 Comments

Adjust for Elevation in Freeman Flow Equation?

11/5/2024

2 Comments

 
Hi all, I am looking for a sanity check on a water supply calculation for water main with significant elevation delta.

We ran a hydrant test on a dead-end run for a new development that is fed from a city main at the top of a hill.

The two furthest hydrants were tested, the flow hydrant at the dead-end and pressure hydrant mid-way down the hill.

City Main = EL 500
Pressure Hydrant = EL 450
Flow Hydrant = EL 400
Proposed FFE = EL 425

The Freeman Flow equation bases hydrant flow on pitot pressure (PSIG) which is relative to the hydrant elevation. To calculate R20 (ie 20PSIG) at that hydrant elevation we use a ratio of PSIG values from the pressure hydrant normalized to 1.85 power multiplied by the hydrant flow rate from Freeman equation.

It is at this point that I begin second-guessing: the ratio that is being used does not take into account the elevation delta as it is PSIG. I have calculated the HGLs for the three pressures based on converting PSIG at its respective elevation.

My initial thought is that the pressure hydrant PSIGs (based on EL 450) should be converted to PSIGs at the flow hydrant (ie based on EL 400) by means of HGL - Hydrant Elevation and then using those "adjusted" PSIG static/residual values as the scaling terms for R20 at the flow hydrant. Then to get a theoretical R20 for a future hydrant at FFE I would repeat the same process, this time normalizing pressure hydrant static/residual HGLs to FFE elevation, holding the Freeman Flow value constant, and using a "new" R20 = 20PSIG at FFE.

​On the face I get reasonable values, but would like to get feedback from the group. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Commodity Class for Sealant Tubes in Boxes?

11/4/2024

8 Comments

 
I am looking for a little help with a storage commodity.

We have a client that is adding in-rack sprinklers to an existing sprinklered facility and is planning on storing tubes of Adseal 1940 adhesive sealant in boxes, in racks up to 15ft.

According to the MSDS sheet
, it is a solid (paste) that is primarily made up of Calcium Carbonate, which in itself is non-combustible, and the flammability hazard rating is “(1) Slight”.

The existing hydraulic placard indicates the existing system was designed to a density of .29/2000, which is about equivalent to Single-Double Row Rack Storage of Class I-IV Commodity per NFPA 13, 2019 edition:

Per Table 21.4.1.2 and Figure 24.4.1.2(d), 8ft aisles and 286 deg F sprinklers, the base design density would be +/- .495/2000. Then, applying a 60% reduction of the density for 15-ft high storage, the final design criteria would be .297/2000.

My only concern is that the commodity would be classified as a Group A Nonexpanded since there is a huge jump in design density. Per NFPA 13 2019 Table A.20.4(b), it mentions that “Bottles or jars (except PET) up to 1 gal containing noncombustible solids” are classified as Group A Nonexpanded. It also calls out such things as “Powders, non-combustible in plastic bottles or jars up to 1 gal; cartoned” as Class IV commodities.

So, I am kind of on the fence on this one between Class IV vs Grp A.

Has anyone ran into having to protect adhesive sealants before or anything similar and would be willing to share their decision process?

​Thank you in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Thank You Top October 2024 Contributors!

11/1/2024

 
Thank you for ending the month with some great discussions! Special shout-out to our Top Contributors in October 2024:
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

Is Node Analysis Report About the Demand Calc?

11/1/2024

4 Comments

 
For those of you familiar with the HyrdraCalc program; does the Node Analysis section on the calculation report detail the demand that the sprinkler system requires?

Or does it list the current calculated condition of the various nodes of the sprinkler system?

I recently received two reports from a consultant that used HydraCalc to show the current conditions with an existing fire pump, and the 2nd report shows the system with a proposed increased capacity fire pump. On both reports, the Node Analysis showed the same parameters for each of the nodes when compared to each other.

As an example, Node 1 (existing pump report) Pressure at Node – 7, Discharge at Node 14.82. Node 1 (new increased capacity pump report) Pressure at Node – 7, Discharge at Node 14.82. It was explained by the consultant that the Node Analysis page details the demand that the sprinkler system requires which is why both reports show the same parameters.

Not being familiar with this program, I wasn’t 100% sure if the explanation was correct.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT