MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Use Fire-Rated Construction in lieu of Sprinklers?

10/31/2024

14 Comments

 
Is fire-rated construction ever enough to not warrant sprinkler protection?

Is there a NFPA 13 section that would validate this one way or another?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Where are PRV Hose Valves Req'd in a Highrise?

10/30/2024

8 Comments

 
How would you recommend determining when PRV hose valves should be used in a highrise?

I am designing a 12-story hotel. The highest outlet is at 125'-5".

Our flow test is mid-50's static and residual at 1,500 gpm. I did the standpipe calculation using a combined source of the city and fire pump. I sized the pump to what the demand was at 750gpm @ 174.26 psi. In turn I put in a 750gpm @ 125psi fire pump and had a 6.45lb buffer.

Do I then do another calculation to find out the maximum static pressure available on the supply side at each level and minus out the elevation loss?

Can anyone give me a guide on how to find out which level needs a PRV FHV and which doesn't?

​Thank you in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Sprinkler Pipe Auto Shutoff in Tornado Shelter?

10/29/2024

6 Comments

 
I am designing a community tornado storm shelter and per ICC 500, Section 309.1, any penetration of the shelter envelope by a liquid line is to be provided with an automatic shutoff.

​How is this being achieved with sprinkler pipe penetration?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Sprinklers for Continuous 3'-10" Cloud Ceilings?

10/28/2024

5 Comments

 
When is a cloud ceiling a ceiling, and when is it an obstruction?

I have a project with a 2-story lobby that has a mezzanine waiting area and clouded ceilings. The clouds are 3'-10" wide continuous clouds that run east/west across the room.

The rows of clouds are spaced 4'-0" apart from each other but will have lights and diffusers between them serving the space. Spacing between the clouds and the wall varies but narrowest dimension is 2'-0".

Even better, the roof above the cloud ceiling is sloped greater than 2/12" and will require an increased design area and sprinklers at the peak. The architect's intent was to not require sprinkler coverage below the ceiling clouds and consider them an obstruction not wider than 4'-0".

I am not as comfortable with this but wanted to bring it up for discussion. I did see a forum post about this come up in 2022 but was wondering if anyone had additional comments. Thank you!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Reliability, Variety of Concealed FA Appliances?

10/25/2024

11 Comments

 
Concealed Fire Alarm Devices: I am looking into specifying concealed fire alarm devices for a project. I have two major questions:

1. Are concealed fire alarm devices reliable?

I have heard second-hand that concealed fire alarm devices do not always function.

2. Are there a variety of manufacturers? I did a quick Google search and have only been able to find one manufacturer.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Check Valve OK on the Pump Discharge Flange?

10/24/2024

4 Comments

 
Can a wafer check or grooved check valve be installed directly on a fire pump discharge flange?

I've found they affect the pump performance by 3 to 8 psi.

When testing we found this true and moved it by a foot. The pump didn’t hit its curve and was fairly new.

Shouldn’t NFPA 20 or manufacturers be aware of this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Are Pictogram Exit Signs IBC & IFC Compliant?

10/23/2024

6 Comments

 
As many/most of us know, there's an internationally standardized pictogram (symbol) for exit signs that's common in many countries worldwide. However, it's not yet common in the US, likely due to what appears to be a misconception that the IBC/IFC only allows "EXIT" lettering.

IBC/IFC Section 1013.5 requires internally illuminated exit signs to be listed to UL 924. (There's a different section on externally-illuminated exit signs, 1013.6.1, that specifies "EXIT" lettering, however, the vast majority of exit signs are internally-illuminated and therefore not subject to anything under 1013.6 due to that section's scope clause.)

UL 924 was revised a while back to allow the internationally standardized pictogram, including in lieu of "EXIT" lettering. (see section 42 of UL 924) Therefore, my impression is that a UL-listed internally-illuminated exit sign that uses the internationally-standardized pictogram complies with the IBC/IFC. (There are such products currently on the market.)

Are UL-listed internally-illuminated exit signs using the pictogram in compliance with IBC/IFC?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

C-Factor for a 55-Year Old System with Debris?

10/22/2024

11 Comments

 
Hydraulic Upgrade to old wet and dry systems and determine "C" factors to be used. Question:

We plan to upgrade a fire sprinkler system from a Pipe Schedule Ordinary Hazard system with k-5.6 standard response heads to 0.25/2000 sqft with k-8 sprinklers, what "C" factor should be used?

The system is 55 years old
and has a good water supply that would easily work for a new system using a C=120; however, debris has built up in the pipe, and if we were to do a hydro-pneumatic flush, the roughness would be much worse than that of new pipe.

The AHJ has no answers other than to do what we feel is best, and the insurance company just wants to see the density increased and "proven" to work at 0.25/2000. Furthermore, there are 2 dry systems that are 55
years old, and they want these upgraded, too. Even if we add a pump, it's just going to slam the sludge to the end of the lines and plug up any new heads that are installed.

Do you have any thoughts?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Why is 90-Minute Door Allowed in 2-Hr Barrier?

10/21/2024

7 Comments

 
Does anyone know the historical context of why a 90-minute door is permitted on a 2-hour barrier?

Why the 30-minute difference?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Pipe Size for Sprinklers Above & Below Ductwork?

10/18/2024

7 Comments

 
Doing a mechanical machine room, and I need to add sprinkler coverage above and below ductwork.

I was told that if you have 2 sprinklers (one covering above the ductwork and one covering under the ductwork), you can run 1-in pipe to each.

So here is the example: I have 4 sprinklers coming off a branchline but 2 of those are under ductwork. The uprights that are above and below are covering the same area.

What pipe size do I need to use for this branch line?

What code justifies this one way or another?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Incidental Storage in FM Req' Storage Sprinklers?

10/17/2024

4 Comments

 
I am designing a sprinkler system per FM requirements.

I have areas containing storage within non-storage occupancies, therefor I'm following FM Global Data Sheet (FMDS) 3-26. The storage area meets all of the limitations of Incidental storage.

My question is, if the hazard class of the space is deemed HC-1 or HC-2, are the sprinklers protecting this area required to be FM-approved storage-type sprinklers...aka K11.2 sprinklers?

If so, this would then tighten up my spacing to 100 sf?

My ceiling is 11'-0. Thanks in advance for any help.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Phantom Flow for 4-Sprinkler Fire Pump Room?

10/16/2024

10 Comments

 
I am working on a project with a diesel fire pump room that is Extra Hazard 2 (0.4 gpm / 2500 SF). The room is only 300 SF, which is well below 2,500 SF.

The 2022 Edition, NFPA 13 28.2.4.2.4, indicates following a set of steps shown in A.28.2.4.2.4. This section indicates that if the flow is less than the minimum required flow, then the difference in flow must be added to a node on the system. A.28.2.4.2.5 shows a picture example of where to add the flow.

The current design has 4 sprinklers within the room, each discharging around 30 gpm ((0.4 gpm x 300 SF) / 4). When reviewing the shop drawings, 880 gpm was added to a node, increasing the system pressure to about 150 psi!

How is NFPA 13 28.2.4.2.4 supposed to be accurately calculated within the hydraulic calcs?

Do you create an imaginary system and, in this case, add 21 more sprinklers for a total of 25 (2500 / 100 SF per sprinkler)?

Adding the 880 gpm to the system shown on the shop drawings and getting a required pressure of about 150 psi doesn't seem right.
Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Is 'Cold-Solder' Spraying Sprinkler or Area Below?

10/15/2024

7 Comments

 
Does 'cold solder' specifically mean that one sprinkler gets another wet, or does it mean that one sprinkler keeps the floor area cool enough so the adjacent sprinkler doesn't activate?

Or is it both?

I've recently had several conversations
in which the other party was convinced that cold-soldering can​ only occur when one sprinkler wets and cools another sprinkler's thermal element.

I was taught a long time ago that cold-solder referred to one sprinkler keeping the floor area wet and cool but not wet enough to effectively put out or control a fire, thereby allowing the fire to 'skip' to the next sprinkler, allowing the fire to grow larger than had both adjacent sprinkler heads activated properly.

Obviously
, if a sprinkler gets wet and does not activate, it causes the same problem. It makes a difference in my mind because, at soffits or varying ceiling elevations, the lower sprinkler could spray into the higher sprinkler's floor area. If the vertical change is 36" or greater, NFPA says to treat it as a wall, and sprinklers must be 1/2 x S from this plane.

In my mind
, the differences in ceiling height would effectively create a baffle, and neither sprinkler would actually wet the other. However, if they were closer than 6'-0 measured on a flat horizontal plane, they would still be cold soldered since one sprays into the floor area of another. I see this all the time. Do you have thoughts on this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Fireproofing for Column on Exterior of Exit Stair?

10/14/2024

7 Comments

 
This is a corner exit stair in a 2-story Type II-B building. There is 2-hr fire separation per client request (only 1-hr by code).

There's one column in the corner that only supports exterior precast walls and roof structure. Does it need to be fireproofed?

I would assume it doesn't. Any ideas? Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments

Taking on Additional Responsibility as NICET 3?

10/11/2024

6 Comments

 
I have 18 years of experience in sprinkler design, and I have a NICET Level 3 certification.

The company
I work for is asking me to hold the License in three states because the previous holder is leaving. I have read the verbiage stating I would be responsible for everything, including the contracts. That seems scary to me.

In your opinion, is the additional responsibility worth it, money-wise?

I don't want to sell myself short, but I also want to be fair.

Do you have any suggestions or tips on how I should be thinking about this?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Window Sprinkler at Ext. Area Assisted Rescue?

10/10/2024

6 Comments

 
The 2018 IBC, Section 1009.7 for Exterior Area for Assisted Rescue (EAAR) requires exterior walls within 10 feet to be rated 1-hour for exposure to fire from the inside.

​When a window is located within 10 feet of the EAAR, can it be protected with a window sprinkler system?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Occupancy for 2 Sleep Rooms in Office Building?

10/9/2024

12 Comments

 
What occupancy would you classify two sleeping rooms in an office building (otherwise B Occupancy)?

The area of the two rooms is 400 sf, and the area of the offices is 6,870 sf.

Will the rooms be R-2? Does the building need sprinklers as a result?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

How to Fix a Flowswitch that Cycles?

10/8/2024

6 Comments

 
We have an instance of "flowswitch cycling" on a new wet-pipe system. The RPZ backflow is thought to be causing the flow switch to fluctuate and, therefore, not get us the flow alarm in a timely manner or at all.

We have opened the manual high point air vent and flowed for several minutes with no success.

Has anyone had this
or found a solution to it?

Potter has a technical bulletin on this but does not go into detail about how to resolve it.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

What is Best Practice for Testing Forward-Flow?

10/7/2024

9 Comments

 
Regarding forward-flow testing, I have read that a main drain (if sized appropriately) can be used in place of other means. This was in the 2016 NFPA 13 A.8.16.2.4.2, but I cannot locate it in the 2019 version.

With that, what is the best practice for testing at the time of system acceptance?

Without being able to use a hose monster, is the main drain test sufficient to ensure the backflow fully opens?

Other than hydraulic calculations, how is it proven that we have an acceptable result?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Recommend Antifreeze for Assisted Living Attic?

10/4/2024

10 Comments

 
I have a client who owns multiple assisted living facilities. It's residential construction with attic insulation on the roof trusses' bottom chord, and louvered gable ends with ridge vents.

They have existing wet pipe sprinkler systems in the attic and have experienced busted sprinkler lines in the past. They want to heat the attics to prevent this with electric heaters.

I have done the heat loss calculations and have determined the heating load would be more than their current electrical service can support. The only options I see available are heat trace, anti-freeze, or conversion to a dry system. Anti-freeze with
UL-listed anti-freeze was my first thought, but it looks like a backflow preventer would have to be added.

Does anyone have experience with this and/or have recommendations on how to address this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

When Does Common Path Stop for Wide Areas?

10/3/2024

6 Comments

 
I understand the definition of the "Common Path" from Section 3.3.49 in NFPA 101, but within the examples it is up to the point when you reach a corridor and have the two exit alternatives.

In a case like the one in the image shown below, the orange area is very wide, or open space, up to where they would measure the common travel distance.

At what point does the path of common travel stop in a scenario like this?

​What is that threshold?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Use Sidewalls in a Room With Sloped Ceilings?

10/2/2024

8 Comments

 
Is there any way to install sidewall sprinklers in a room with sloped ceilings?

Say
you had a rectangular room with a ceiling attached directly to the underside of a traditional gable roof with a high ridge peak in the middle. Concealed pendent ceiling sprinklers are often not possible ​because the space above the ceiling is completely filled with insulation.

Can you do sidewalls on the vertical walls near the ceiling high point to protect the room?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Thank you to Top September 2024 Contributors!

10/1/2024

 
Thank you to everyone for sharing your expertise and making this community stronger. Special shout-out to our Top Contributors for September 2024—you keep this place awesome!
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

Does OSHA's Clearances Apply to Backflows?

10/1/2024

4 Comments

 
Do OSHA safety regulations apply to RPZ and DCDA backflow preventers?

OSHA requires 30 inches to the face off a side wall for maintenance for horizontal installations.

My contention is
 that if the drain to the RPZ runs to that wall, you will have an obstruction and trip hazard, and it will not be accessible for maintenance.

I've also installed the RPZs 4 feet above the tight pump room floors for access. It's never been a problem.

Please advise. IBC says to install backflow preventers according to the manufacturer's instructions.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT