MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

"Pipe Schedule System" OK on Hydraulic Placard?

5/30/2025

14 Comments

 
A number of board and care facilities have​ missing hydraulic placards. It's possible they never had them since the sprinkler system was installed before placards were required.

They are now required, and I
wonder if it would be a viable option to survey the system, get pipe diameters and sprinkler counts, and see if they fit within the criteria of the pipe schedule method?

If it does, would there be any issues stating so on the hydraulic placard?

The board and care facilities range from 3 - 16 bedrooms and no more than 2 stories high.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Reason to Omit Bypass Around PRVs in Series?

5/29/2025

4 Comments

 
A fire pump supplies a combination riser for sprinklers/standpipes.

Between the combination riser and the fire pump, there are 2 pressure-reducing CLA VA in series. It appears that 2024 NFPA 14 10.2.5 requires a bypass assembly for these 2 CLA VA.

​Is there any reason or justification to delete this bypass around the CLA VA assembly?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Still Need Aerosol with Auto-Smoke Testing?

5/28/2025

1 Comment

 
In reference to the 2025 edition of NFPA 72, Table 14.4.3.2, Item 17(7)(a), it is stated that "manufacturer’s published instructions that ensure smoke entry from the protected area, through the vents, or into the sensing chamber" may be used, which appears to include self-testing smoke detectors such as the Honeywell self-test series.

These detectors introduce a small quantity of smoke or aerosol into the sensing chamber as part of a built-in functional test sequence. It is my understanding that this self-testing technology may fulfill the requirement for a functional test that traditionally uses an aerosol can to verify smoke entry and detector response during both initial acceptance and annual testing.

Further, Section 14.4.4.2 states that “If automatic testing is performed at least weekly by a remotely monitored fire alarm control unit specifically listed for the application, the manual testing frequency shall be permitted to be extended to annually in accordance with Table 14.4.3.2.”

However, this section does not explicitly clarify whether this weekly automatic testing relates to the smoke detector’s functional test, sensitivity test, or both.

With that context, I would like to get clarification on the following points:

Does NFPA 72 (2025) permit the use of self-test smoke detectors that introduce a small amount of test smoke into the sensing chamber to fully satisfy the functional testing requirements (including smoke entry testing) for both initial acceptance and annual testing per Table 14.4.3.2?

If an approved self-test detector performs an automatic internal functional test that verifies smoke entry into the sensing chamber and provides results to a remotely monitored fire alarm control unit, does NFPA 72 still require a manual smoke entry test (e.g., aerosol can) for annual testing purposes?

Does the reference in Section 14.4.4.2 to “automatic testing performed at least weekly” apply to functional testing, sensitivity testing, or both?

And is there any mandate elsewhere in NFPA 72 requiring weekly testing of smoke detectors?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

Sprinkler Height & Put Above a Sloped Ceiling?

5/27/2025

3 Comments

 
I have sloped steel decking on Glulam Beams 11" wide x 26" deep to 36" deep. They range from 2'-2" to 6'-0 wide in a light and ordinary hazard community center setting. I have areas with ceilings below as well.

Do I need above and below sprinklers due to the wood beams?

Do I need to have heads between the beams up to a 12" deflector distance in areas without ceilings?

The 22" deflector depth doesn't make a difference in this instance. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
3 Comments

Type of Fire Protection for Existing Server Room?

5/26/2025

8 Comments

 
We have an old server room. The server room is split into two side-by-side rooms separated by a wood stud wall with sheet rock covering. One server room side is approximately 15'x30'. The other side is approximately 30'x30'.

The ceiling is a 2 ' x2' square ceiling tile with insulation above. Above the ceiling is open to the warehouse.

The floating floor is suspended approximately 12". Wires for the servers are under the floating floor resembles a bird's nest. The wires also protrude through all four walls at various locations, but mainly between the floating floor and the concrete floor. The old sprinkler system needs upgrading.

We are thinking of a clean agent system, but the cost would be monumental. Moving the server room to a different location would also be cost-prohibitive. Both server rooms would require doors, walls, and ceiling modifications including rewiring all the server equipment for a clean agent system. We have a large amount of server equipment.

Does anyone have fire protection system(s) suggestion?

Does anyone have reference material for suggestions on installing different systems to provide to upper management?

What is the best method for providing a cost estimate for various types of systems?

Also, has anyone had luck with the misting system in server rooms?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

OK to Acoustically Seal Sprinkler Penetration?

5/23/2025

11 Comments

 
We are converting a 1930s church to a live music venue. To prevent noise, we are sealing the roof in the attic and insulating the ceiling in the attic.

The fire sprinkler pendants were installed through the existing plaster ceiling with oversized bore holes. Additionally, the pendants have a metal collar with 4 integral slots.

Is it permissible to seal the oversized bore hole?

Is it permissible to seal the upper terminus of the slotted metal collar?

​We're not looking to violate code but address the sound needs. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
11 Comments

Shelves in a Changing Room Considered Storage?

5/22/2025

4 Comments

 
We have a room that will be used to store clothes within a changing room. The facility is a place of worship.

The owner is planning on 4' wide by 8' long
free-standing storage shelves. We just discovered that the unit top will be only 4" below the ceiling. The room was planned for light-hazard​ concealed sprinkler protection.

So, would you consider this storage?

Or would you look at the shelving unit as an obstruction?

In retail, we would limit the height of the unit to be 18" below the ceiling. But I'm not sure how to protect this build. 

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
4 Comments

Recessed Building Entry Ceiling 2-Hr in Type III-B?

5/21/2025

3 Comments

 
We have a building that's Type III-B construction.

Does a recessed building entry's ceiling need to also be 2-hour fire resistance rated, and non-combustible?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Which Hydrants Count for Available Fire Flow?

5/20/2025

7 Comments

 
When calculating a risk score on an occupancy, a question asked is "Is fire flow available?"

My question is this: which hydrants does everyone count towards being available?

IFC 507 states that if a hydrant is not within 400-600 feet, then an on-site hydrant is required. Some of my colleagues interpret that as "Anything outside of that radius does not count as available for Fire Flow."

We carry 1000 ft of supply hose, so some say all hydrants within a 1000 ft radius contribute. However, that is really to dress a single hydrant up to 1000 ft away, not to dress multiple hydrants within 1000 ft. Ultimately, we get to decide in the end, but we want to make an informed decision and document our methods for consistency.

This question is not about calculating the needed flow and assumes the water department can provide accurate flow data for each barrel.

​Any insight from the pros and other AHJ's would be fantastic. Thank you for your time.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

What is Effective Capacity of Water Storage Tank?

5/19/2025

5 Comments

 
How do you determine the effective capacity of a water storage tank for fire protection purposes? 

Where are the unusable limits set for the bottom of the tank suction and the top air gap?

​Is there a mandate for either of these in code or standards?

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Does a Lint Filter on Roof Require Fire Sprinklers?

5/16/2025

2 Comments

 
We have an MLF-1015 Lint Collector on a roof.

Does it need fire protection?

​I have never covered one yet. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

At What Level Should Diesel Tanks Be Refilled?

5/15/2025

4 Comments

 
Diesel fuel tank - how low should I allow the diesel fuel level to drop before I fill the tank with diesel fuel for a fire pump?

Should
I add diesel fuel when the fuel gauge drops to 3/4 full, 2/3 full,​ or 1/2 full?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

More Design Criteria for a Slope Exceeding 4:12?

5/14/2025

5 Comments

 
I understand that sloped ceilings are those that exceed a 2:12 pitch.

NFPA 13, 2025 edition, Chapter 19.2.3.2.4 (3) & (4)
mention ceiling slopes that do not exceed 4:12. This leads me to believe that there are additional criteria for ceilings exceeding 4:12 pitch.

Is anyone aware of additional criteria regarding design criteria where ceilings exceed 4:12?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Trapeze Support with 3 Attachment Points?

5/13/2025

3 Comments

 
How would you go about designing for a trapeze supporting (2 or more) 6" mains over large spans?

For example, you have a 16'-0" trapeze span, your truss is every 8'-0". Your idea is to place one long trapeze across 16'-0" to support 2-4 feed mains treeing from a riser manifold.

NFPA 13 says we double the section modulus for every pipe, but that is assuming the we are using (2) attachment points; it doesn't seem to explain different configurations like attaching at 3 or more points on the structure.

How would we go about designing for this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

One Water Storage Tank for Two Buildings?

5/12/2025

6 Comments

 
Existing remote church with water provided by a storage tank. The church plans on building a separate meeting hall that does not connect to the church. These buildings will be approximately 200 feet apart. This new building will require sprinkler protection.

Is it possible to use the existing storage tank to serve both buildings?

​The current tank is sized just for one fire area, so
it is not for two simultaneous fires. Normally, two separate buildings have two services, but I wonder if there is an exception for storage tanks in remote areas.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Are There Any Listed "Cheater" Extension Fitting?

5/9/2025

8 Comments

 
NFPA 13, 2016 Section 6.4.8 permits using extension fittings ("cheaters") for sprinklers K8 or smaller.

Does anyone actually make a listed cheater?

There are multiple manufacturers/suppliers that sell them, but none of them appear to be listed.

I see the benefit of using small extension fittings that don't impact hydraulic calculations (per Section 6.4.8.5.1) when ceilings are installed at the wrong elevation, but I don't see how you can use them if they aren't listed per NFPA 13, 2016 Section 6.1.1.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Use QR & Residential in Same Compartment?

5/8/2025

8 Comments

 
Renovating an 11-story hotel using residential sprinklers in accordance with NFPA 13 (2019).

Calcs based upon S x L (4 sprinklers at .10 density) or manufacturer data sheets (which ever requires greater demand).

Sprinklers need to be 175° due to less than 24" from the side of the wall mount diffuser. There are a few rooms that require a SW throw of 20'-4" (22'-0' per data sheets). However, many manufacturers do not manufacturer this 22 ft throw in 175°, only 155°.

Can I use a quick response (Viking VK630) SW that throws 22 ft along with the residential sprinklers in the same compartment?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments

In-Rack Sprinklers Allowed Just Outside the Rack?

5/7/2025

9 Comments

 
We are protecting a single row storage rack that is located beside a wall. The distance between the face of the storage rack and the wall is approximately 18". We are installing in rack sprinklers.

Can the line of in-rack sprinklers be installed along the face of the single row rack, between the storage rack and the wall?

​Or must the line of in-rack sprinklers be located inside the storage rack?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

NFPA 13R System with 3/4" Domestic + Tank?

5/6/2025

9 Comments

 
I'm designing a 13R system. The building currently has a 3/4" domestic water service. The building is in a location that would make installing a new (larger) service a logistical nightmare.

Is it allowed to connect the 3/4" existing supply to a water storage tank (sized per system/domestic demand) in the basement, then build a residential riser from that?

If this is allowed, do I only take my calculations back to the storage tank?

Do you foresee other problems with this? 

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Connect 4-in FDC Feed into 2-in Sprinkler Main?

5/5/2025

10 Comments

 
When connecting a FDC to a system at a point other than the riser, is it acceptable to connect a 4 x 2½ x 2½ (2-inlet) FDC using 4" pipe feed for the FDC and tying the 4" pipe to a 2" sprinkler main?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Draft Curtain Measured to Ceiling or Sprinkler?

5/2/2025

6 Comments

 
When using a draft curtain and closely spaced sprinklers at a floor opening for an exit access stair, what is the 18" depth for the draft curtain measured to?

The adjacent ceiling surface, or the deflector of the sprinkler?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Thank You to Top April 2025 Contributors!

5/1/2025

 
​Thanks for sharing your thoughts and improving the industry! Celebrating April 2025's Top Contributors:
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

What does a Jockey Pump Expansion Tank Do?

5/1/2025

3 Comments

 
I have a private fire main serving a large manufacturing building. The fire main is served by a city connection and has an electric and diesel fire pump before returning underground and surrounding our building. The jockey pumps have a connection to a Jockey Pump Expansion Tank, and I have no idea what this is intended to do.

Does anyone have similar equipment or know what a Jockey Pump Expansion tank does?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT