MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Temporary Sprinkler Protection in a Hospital?

1/30/2026

11 Comments

 
We have encountered a situation not fully addressed before in our jurisdiction.

Scenario: Existing fully sprinklered hospital having renovation work done in multiple areas and floors. Some phases of work take months, others take 6+ months to complete. After ICRA walls (Infection Control Risk Assessment / temporary walls to isolate construction areas) are installed, the GC will remove the existing ceilings and commence with architectural demolition.

At that time, we (sprinkler contractor) came in and removed the existing pendent sprinklers and replaced them with upright heads on short 3" sprigs (without regard to obstructions or distance down from structure). This is due to existing MEP trades yet to perform their scope of work, ie: HVAC, Plumbing demo, then new install.

NFPA 241 indicates that the temporary upright sprinklers need to be installed with regards to the obstructions per NFPA 13.

At this phase of construction, that would necessitate installing the upright sprinklers for ductwork that is scheduled to be demolished in a few weeks along with other MEP trades.

By following the sprinkler obstruction rules of NFPA 13, the net effect is that we would constantly be relocating the temporary protection at the same time each trade completes a portion of their work. This issue has just arisen recently based upon an AHCA site visit (Agency for Health Care Administration). Prior installations of the uprights without obstruction spacing rules has not been called out.

​How has this issue of temporary sprinkler protection for buildings under renovation been delt with by others?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Curtain/Vestibule for Existing Highrise Elevator?

1/29/2026

1 Comment

 
I am the third-party reviewer for an existing building that is a high-rise but does not have elevator pressurization.

If this were a new building, IBC (2021) Section 3006.3 would apply. But, this is an existing building, and the work qualifies as an Alteration Level 2. The primary engineer says that since the freight elevator is within the work area (although not being touched), per IEBC 801.3, the client will need to install either elevator curtains or a vestibule to keep smoke out per Section 3006.3.

I am of the opinion that since they aren't touching the elevator, I think the IEBC 803.1 is a stretch, and the fact that per Exception 5 of the Vertical Openings Section (803.2.1), the elevator isn't even required to be enclosed. (I do think
it's a good idea though, and it's not like it's every floor, only their project space would get curtained.

This is purely a code required question, though.

Does an existing high-rise with Level 2 Alteration trigger smoke management here, even though the elevator is not altered?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

How to Select the Coverage Area for a Sprinkler?

1/28/2026

10 Comments

 
We have an apartment, protected by a birdcage residential sprinkler system per NFPA 13. We need to calculate the most demanding 4 sprinklers, which end up being 3 in the room and another on the back side of one of the 3 (this apartment has the longest throw).

I need to calculate the most demanding of the two (1) flow rates per the approval chart in the sprinkler's listing, or (2) calculate based on 0.10 gpm/sqft over design area according to 8.5.2.1 or 8.6.2.1.2.

Can I choose 8.5.2.1 or 8.6.2.1.2? Or is it the more demanding of 8.5.2.1 or 8.6.2.1.2, and then compare that to the flow rates per the approval chart in the sprinkler's listing?

Thank you in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Seismic Req'd on Fire Pump Suction & Discharge?

1/27/2026

2 Comments

 
Haven't come across this one before - are the horizontal pipes, both suction and/or discharge from a fire pump, required to be seismically braced?

We have seismic bracing required for the building and a review comment to assess bracing for the fire pump suction and discharge. NFPA 20 and 13 both don't seem to speak to it, but perhaps I am missing something.

What is code required for seismic on these two runs?

Thanks in advance.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Sprinkler Design Area for Rack Storage?

1/26/2026

3 Comments

 
In NFPA 13 (2025), where does it show what AREA discharge is needed for the Rack Storage tables?

I'm looking at Table 21.4.1.2.1 for Class II, up to 15", 8-foot aisles, and it says a density of 0.22 for ordinary temperature sprinklers, but what AREA?

It happens that this is inside a cooler (44 degrees F), which is why I am not looking at the high-temperature values.

Any assistance appreciated. Anything else I should know?

In CA
, we are just starting to use the 2025 Edition, so it is new to me!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
3 Comments

Can ESFR Sprinklers Remain Above Lower Office?

1/23/2026

6 Comments

 
I have an ESFR-protected warehouse. The General Contractor is putting in offices with grid ceiling. A full-height demising wall separates the warehouse from the newly constructed office space. Heads are being dropped from the branchlines at deck height to the new grid ceiling.

Are the ESFR sprinklers above the new office ceiling required to be plugged by code, or can they remain in place?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Design Area for Hotel Utility/Mech/Elec Spaces?

1/22/2026

4 Comments

 
I'm designing a sprinkler system for a hotel. The layout is pretty standard with hotel rooms and corridors, but on one end of the corridor is a "suite" of utility/maintenance rooms.

The rooms are labelled as "Housekeeping" (260sf), and through that, "Electrical" (70sf), and "Linen Chute" (30sf). All walls are 1-hour rated. I am calculating them as Ordinary Group 1.

My question is: How do I determine the design area?

Can I calculate just the Ordinary Hazard spaces like a Room Design method, or would I calculate the Ordinary Hazard spaces plus four corridor sprinklers?

Or does it need to be 900 sf (1500 with QR reduction)?

Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Omit Sprinklers in Partial-Insulated Attic Space?

1/21/2026

8 Comments

 
We are the Engineer of Record (EOR) with an RFI for building in the substantial completion phase of construction.

The contract documents called for delegated fire protection design. The working drawings called for upright sprinklers in the combustible concealed space above a vaulted ceiling.

Instead of installing the uprights, it was agreed by the fire protection sub and general contractor that the space would be filled with insulation.
The FP contractor's engineer, who prepared the working drawings, observed that the concealed space was not completely filled per NFPA 13 requirements. The architect has deemed that fire sprinklers are not required for this building due to the square footage. The rest of the entire building is fully covered.

Can the combustible concealed space between the vaulted ceiling and the roof be considered a portion of the building that is not intended to be covered by sprinklers?

Meaning per New York State (NYS) Fire Code (FC) 901.4.2, the building is partially furnished for protection?

Or, is the combustible concealed space considered part of the open room assembly, meaning it must meet NFPA 13 requirements since the vaulted ceiling for the room space is protected by pendent sprinklers?

Our initial reaction is that if sprinklers are provided and not required by the NYS Building Code, then the system would be considered required per NYS FC 901.4.1 and would need to meet the requirements of NFPA-13.

​What are your thoughts?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
Observation of insufficient insulation in concealed space.
Picture
8 Comments

How to Address Fire Pump with Poor Supply?

1/20/2026

17 Comments

 
We have a disagreement on a fire pump installation. Flow test shows 42 psi static, 10 psi residual at 475 gpm from an 8" municipal main.

The fire sprinkler contractor plotted the water supply curve and says it cannot support the specified 1,000 gpm @ 100 psi pump; they're refusing to certify the fire pump without a suction tank or another resolution.

The mechanical engineer argues the 8" main at 42 psi static should theoretically deliver way more than 1,000 gpm and questions whether the flow test results accurately represent what the pump will actually see at its suction connection.

The steep pressure drop (42 psi to 10 psi in only 475 gpm) seems abnormal for an 8" main.
The area has aging infrastructure and known low-pressure issues.

Looking for the community's input on: (1) 
Is the fire sprinkler contractor correct to base their analysis on residual pressure under flow conditions, or should we be looking at static pressure as the mechanical engineer suggests?

(2) What's the correct NFPA 20 methodology for evaluating water supply adequacy for a fire pump?

(3) When you see such a steep pressure drop in a flow test, what are the typical causes and how would you approach resolving this?

What solutions have worked for others dealing with marginal municipal water supplies?


Thanks in advance.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments

Minimum Aisle Width for Racks with ESFR?

1/19/2026

2 Comments

 
Is there a minimum aisle width for racks using ESFR sprinklers?

​I see there are a couple of areas where they mention min aisle widths, but they are not common situations. I also see in the manufacturer's data sheets, but those are only for the larger sprinklers K25 & above.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Economical Tank for 30k Gallons Prone to Freeze?

1/16/2026

7 Comments

 
Anyone know of an economical way to store 30,000 gallons of Fire Sprinkler water above ground in (2) 15k or (3) 10k poly tanks stored outside in area that can get below 0 degrees in the winter?

1) Can these tanks be insulated?

2) Can these tanks be equipped with immersion heaters?

3) Do these tanks degrade when exposed to the sun?

Ideally, we are pushing the client to consider building a structure or Lean-To with some heat to solve all of these questions.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Electric Valves Replace Deluge in Foam Systems?

1/15/2026

1 Comment

 
Can electric valves be used to replace deluge valves in foam systems?

​NFPA 11 does not seem to prohibit this practice. Other than their relatively slow actuation time, electric valves have no significant drawbacks.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

Fire Pump Test Loop Connect Upstream of OS&Y?

1/14/2026

5 Comments

 
NFPA 20 (2019) Figure A.4.22.1.3(b) provides a typical diagram indicating pipe for fire pump test connections. In this detail the flow meter loop is shown to return to the suction side of the pump and connect between the fire pump and the suction side OS&Y control valve.

I have seen installations over the years
 where this connection is placed on the inlet or city side of the OS&Y. This seems to simplify the loop arrangement. Functionally, it would seem to be similar as you would need the OS&Y open to allow some cooling water to reach the circulation relief valve.

Is there anything in NFPA 20 that would prohibit this arrangement?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Sensing & Air Lines Need Be "Listed for FP?"

1/13/2026

4 Comments

 
In order to use pipe and fittings, they need to be "listed for fire protection service."

Do fire pump sensing lines need to meet this listing?

What about compressed air lines coming from the air compressor to the air maintenance device, do they need to meet this listing?

What about air on the downstream side of the maintenance device?

We're curious on different methods to install these components where some fittings & pipe combinations are listed and some aren't (such as copper pro-press for sensing lines).

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Thank You to Top December 2025 Contributors!

1/12/2026

 
Thank you for rounding out the year with all of your expertise! Here are our top December 2025 contributors. 
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

IBC 3008 for All Elevators with Occ Evacuation?

1/12/2026

2 Comments

 
IBC 3008.1 states that when elevators are used for occupant self‑evacuation, all passenger elevators for general public use must comply with Sections 3008.1–3008.10.

​The language is unclear: does this require full 3008 compliance for every passenger elevator in the building, or only for the elevators specifically designated for occupant self‑evacuation (e.g., those serving levels above 420 ft / 128  m)?

How is this typically interpreted in super high‑rise buildings where adding an additional exit stair is not feasible?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Attic System Pass with Ground-Level Inspection?

1/9/2026

6 Comments

 
Has anyone encountered situations where a dry sprinkler system had incorrect repairs or installations, but still passed inspection because NFPA 25 allows portions of the inspection to be done from ground level—even though the piping is actually located in an attic?

Is this actually acceptable under NFPA 25? What recourse did you have?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Commodity Classification for Boxed TVs?

1/8/2026

8 Comments

 
What commodity classification would boxed flatscreen TVs fall under?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

What Safety Factor to Use for Fire Flow?

1/7/2026

12 Comments

 
In the absence of a code-mandated requirement, what safety factor ​should we apply when evaluating fire flow, if you apply one at all?

I am currently working on a building that has a code-required fire flow of 2,000 gpm at 20 psi. Using the MeyerFire Toolkit to evaluate the water supply, I found
that the available fire flow is 2,004 gpm at 20 psi.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
12 Comments

Check Valve on Supply with Multiple Zones?

1/6/2026

7 Comments

 
For multiple systems with an FDC, is it still necessary to install a check valve downstream of the control valve on the water supply feed?

If no check valve is installed, will the water flow back to the main water supply pipe instead of flowing to the sprinklers or hose connections when the FDC is in use?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments

Exterior Signage Required for Sprinkler Zones?

1/5/2026

8 Comments

 
I have a 115,ooo sq ft warehouse with a monitored sprinkler system. There is a pump room 200 feet away that has the FACP. The main water supply enters the building, then has three separate risers labeled as system 1, system 2, and system 3.

Is there a fire code that requires the building to have signage on the exterior of the structure indicating where Zone 1, 2, or 3 is?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments

FDC for Each Building in Private Fire Water Loop?

1/2/2026

10 Comments

 
I'm having trouble finding code citations for this, but if a single-owner site with multiple buildings (like a transportation authority property that has multiple separate buildings) has a dedicated fire water loop serving the sprinkler and hydrant water for the site, can they provide FDCs where the fire water ties into the municipal water, and not provide FDCs for the individual building sprinklers?

Or is each sprinkler system required to have its own FDC?

I would imagine that each building with a sprinkler system would still require an FDC, but I can't really find code language about this specific topic.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

MeyerFire Tools - What Do You Want to See?

1/1/2026

9 Comments

 
[from Joe] Happy New Year!

I'm thankful for the community we have here. Just wanted to start off a slow day with a question for you - 

What tools or resources could we be thinking about constructing in 2026? 

What do you want to see more of from us?

Cheatsheets? Tools? Topics? 

Let's hear it. Cheers!

​- Joe Meyer
9 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT