MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Appropriate Density/Area for EH1 Aircraft Hangar?

7/14/2022

8 Comments

 
NFPA 13 required Extra Hazard Group I sprinkler protection for Aircraft Hangars.

What is the appropriate density/area be under CMDA design?

NFPA 409 has a minimum density of 0.17 gpm/sqft (6.9 Lpm) and uses k5.6 to k8.0 quick response sprinklers, however the design area is 15,000 sqft (1,394 sqm).

The hanger is only 9,680 sqft (900 sqm) and three light aircraft are to be stored in the hangar. 

Would 0.30 gpm/sqft (12.2mm) density and an area of 2,500 sqft (230 sqm) with quick response not be more affective than 0.17 gpm/sqft (6.8mm) density and a 9,690 sqft (900 sqm) area?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
M. Newell
7/14/2022 08:11:15 am

If you look at it solely from a discharge perspective.

.3 x 2500 = 750 + 500 hose = 1250gpn

.17 x 9690 = 1647.3 + 500 hose = 2147.3

The discharge from 409 is 900 gallons more water discharged.

Also, if 409 references NFPA 13 for the discharge and not to take hangar area then you would have to add the additional discharge of .17 x 5303 = 901.51 gallons into your calc also.

See NFPA 13 2019 27.2.4.2.4-27.2.4.2.5 - for the additional flow to be added.

Reply
franck
7/14/2022 11:53:31 am

Note that this calculation only applies when different adjacent occupancies with different required densities (or different type of k-factor for the sprinklers) are present : i.e. you want to meet .3 over 2500 over a 2500 sq ft area only, but require .17 over 15 000 sq ft for the remaining area.
Which could be the case if you protect a EH gr 1 hazard on a given 2500 sq ft area and want to protect the remaining of the building with .17
This not seems to be the case in this situation, but rather a choice between.3/2500 for the entire building or .17/15000 for the entire building

Reply
Jesse
7/14/2022 08:25:41 am

I'm confused. Are you protecting the hangar under 13, or are you protecting the hangar under 409?

What Group is the Hangar?

Reply
Anthony
7/14/2022 08:27:11 am

I believe the AHJ/building code would tell you which standard takes precedent and thus which curve to use.

However do note the .17 over 9680 would require more total volume of water thus driving up the size of your riser and mains. The .3 over 2500 would require larger branch lines and heads but limit the size of your riser. So the first approach would best be best if the fire was considered to be a hazard for the whole of the hanger. The 2nd option if the fire was considered to be more likely to be contained to a smaller portion of the hanger and suppression was likely prior to spreading to other areas/aircraft.

.3 gpm/sqft x 2500sqft = 750 gpm
.17 gpm/sqft x 9680sqft = 1646 gpm

Might be worth your time to run a supply calc and see what you end up getting with an extra hazard design over the whole building.

Reply
Dan Wilder
7/14/2022 08:41:18 am

Need to identify the type of hangar first before deciding on a design approach.

Due to things like horizontal fire spread and wing shielding, the larger remote area may be the better choice vs the smaller design and the system being overwhelmed by a spreading fire.

Reply
Eric
7/14/2022 10:33:36 am

Dan's point about horizontal fire spread is really important here.

NFPA 13 densities for both occupancy hazards and storage hazards are generally based around standard combustibles and minimal obstructions.

Unique hazards like flammable liquids, aerosols, aircraft hangers and such have their own codes/standards because they present unique challenges that don't fit within the basic guidelines of NFPA 13. Making assumptions on which fire control approach is "better" is really risky and is the reason why full scale burn tests are performed by FM or the FRR.

Imagine a fire utilizing your proposed EH1 design that starts as a fuel spill underneath an airplane. Perhaps it even catches the bottom of the plane on fire. All this heat release starts activating the QR sprinklers, but hardly any of the water is reaching the fire. I could see this situation quickly overwhelming the system design as more QR heads activate away from the fire center until your design fails.

The alternate design with a lower density over a large area might not be as likely to control/suppress an early stage fire, but will however provide cooling and wetting over the entire area without failing by to many heads opening. This lower level of control may provide enough time for manual fire fighting to begin before things get completely out of control.

I'm not saying your design choice is wrong, but it is certainly something that should be thought deeply on as it is probably the hardest part of industry.

Reply
franck
7/14/2022 11:44:36 am

EH gr 1 only applies to hangars that are not under 409 requirements
If your hangar falls under 409, you need to use .17 over 9680
If not, you can use .3 over 2500

The main reason for a larger area is indicated by Dan. A higher density with a smaller area is not adequate when you expect to open many sprinklers in all cases.

Same approach for turbine buildings (power generation) where the design is .3 over 5000 because of a possible oil poil fire and 3 dimensional fire in the building. It even used to be defined with 2 design that had to be met simultaneously in the past : .2 over 10 000 AND .3 over 3 000, replaced in the late 80s by .3 over 5000 (one demand).

Reply
Tim
7/15/2022 04:54:16 am

Now I see the role of the automatic water sprinklers is clearly to cool other risks in the space. Fire suppression has to be low level in form of LX or MX foam. High density application from the roof will possibly have negative impact on the foam blanket. Its clear now why the lower density 0.17 over 5000 sqft for Type 2 (000) construction is recommended by NFPA 409. Design and hydraulics NFPA 13 the density and area NFPA 409. Low level suppression is a must do if you want to have any hope in successful automatic fire suppression or intervention.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT