I'm looking at the Idle Wood Pallet Table, 20.14.1.2(a) in NFPA 13, 2019 Edition.
Below the table there's a note saying if using 11.2K or larger K-factor sprinkler or high-temperature rated 8.0K sprinkler, the design area can be reduce to 2,000 sqft. But the table notes anything over 6 ft storage require 11.2k sprinklers with various area of operation over the 2,000 sqft. If what I'm reading is correct, is there a reason to use any of the area of operation noted in the table instead of the 2,000 sqft, since I be using 11.2K anyway as required? I feel like that note is only really directed to the < 6 storage height for an option to use 11.2K to decrease the area of operation from 3,000 to 2,000. Is that right? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
8/20/2025 06:20:15 am
Absolutely correct.
Reply
S
8/21/2025 05:51:38 am
We need a like button.
Reply
Joe Meyer
8/21/2025 07:02:04 am
I know, right!? The good thing about this site (this is Joe Meyer) is that its simple and easy to comment - the downside is if I swap out the commenting system it'll require user logins and feel significantly different.
OP
8/21/2025 09:37:53 am
Thank you!
Reply
Jesse
8/20/2025 12:56:20 pm
You are correct. When I was first cutting my teeth in the world I was in Loss Control. I read a big study on idle pallets and the BTU release expected and it was rarther terrifying
Reply