Is there a code or standard that requires inspection or testing, or preventative annual, quarterly or monthly maintenance of smoke management systems?
Is this spelled out somewhere and I'm just missing it? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Chad
12/19/2025 07:30:00 am
All fire alarm interfaces follow 72
Reply
Glenn Berger
12/19/2025 08:08:31 am
NFPA 92 (2024) Section 8.6
Reply
Todd E Wyatt
12/19/2025 08:34:26 am
The scoping Code (e.g. IBC-2024) Section 909 Smoke Control Systems “establish minimum requirements for the design, installation and ACCEPTANCE TESTING of smoke control systems that are intended to provide a tenable environment for the evacuation or relocation of occupants.”
Reply
Todd E Wyatt
12/19/2025 08:35:10 am
REFERENCE
Reply
Jack G
12/19/2025 09:11:48 am
My colleagues really nailed this!! Excellent responses !
Reply
12/19/2025 09:48:50 am
2024 IFC 909.12.1 requires a pre-programmed weekly test to operate all devices, equipment, and components used for smoke control. An exception does apply where such testing will interfere with normal building operation, but this must be approved by the building official.
Reply