Is a fire supply allowed to have any joints, offsets, or fittings underneath the building foundation other than the 90-degree elbow looking up to the flange?
What's the code or standard basis for allowing or not? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
2/5/2026 06:34:47 am
NFPA 13 - Chapter 6 - Section 6.5.3
Reply
Adam
2/5/2026 08:21:18 am
Looking through Section 6.5.3 in the Handbook was a good code-dive this morning!
Reply
Jesseq
2/5/2026 08:09:01 am
Yep Dan is right on the money here.
Reply
Glenn Berger
2/5/2026 08:17:10 am
Dan's response is spot on. There is a provision that trenches can be used if you need to place additional pipe lengths below a building.
Reply
Dave
2/5/2026 10:25:34 am
I think the OP is asking about fittings other than the 90 looking up. I have seen... specs that require the only fitting allowed to be the one 90, but honestly, as wise as that may be, I cannot find that written in any standard - just the 10 ft. limitation.
Reply
Ryan Hinson
2/5/2026 10:53:45 am
To further clarify, the footings are typically at the building edge below exterior walls. Joints are not permitted directly under bottom of the footing. Design prudence generally minimizes joints under slabs though they allowed to 10 ft...without an open, accessible trench. I like NFPA 24 (2022) Figure A.10.4.3.1. If UG joints on the lead-in must be within the building footprint, put them under the slab, with allowable sleeving through the wall above the footing, or in an accessible trench. As has been stated by others, there are other provisions for how to accomplish this with varying degrees of potential facility disruption which need to be considered. Don't forget necessary considerations for the lead-in to be properly- and fully restrained.
Reply