NFPA 13, 2019 Edition, Section 8.6.22 states, "Premixed antifreeze solutions of propylene glycol shall be permitted to be used with ESFR sprinklers where the ESFR sprinklers are listed for such use in a specific application."
Are there any current ESFR Sprinklers listed for use with antifreeze? I am currently only finding obsolete sprinklers that were listed for such use. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
8/26/2025 06:26:51 am
https://www.meyerfire.com/daily/is-esfr-allowed-to-be-a-dry-system
Reply
Brett
8/26/2025 06:38:10 am
I don't know of any ESFR sprinklers that are listed for use with antifreeze. I'm guessing it's not worth getting the listing since antifreeze can only be used with very small systems (< 40 gallons) for storage.
Reply
Anthony
8/26/2025 08:22:42 am
Antifreeze is generally considered the last resort for any system, I'd look at dry systems (Quell by Tyco) or see if a dry pendant head can work.
Reply
Dan Wilder
8/26/2025 09:20:14 am
The sprinkler itself may not state the information, but looking at the systems themselves, they have listed sprinklers noted.
Reply
Pete H
8/26/2025 09:58:37 am
Well struck as always, Dan, thank you for the clarification.
Reply
Anonymous
8/26/2025 11:12:36 am
This data sheet is from 2011, and upon searching Viking's website, I am not seeing this available anymore. Could you provide further information on where this was found?
Reply
Dan Wilder
8/26/2025 02:05:00 pm
You would be correct as to the current lack of available options.
Jose R Figueroa
8/27/2025 04:19:53 pm
The FM Approval Guide does not list any FM-approved ESFR sprinklers for antifreeze systems.
Reply