Any 5-Year Testing for Manual Wet Standpipe?

12/4/2024

3 Comments

 
What is involved in a 5 year inspection/test for a manual wet standpipe?

I see in NFPA 25, 2017 edition that manual wet standpipes are not required to be flow tested or hydrotested when part of the sprinkler system.

So my question again is are there any specific requirements for 5 year testing for manual wet standpipes?

​Thank you all!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Pete H
12/4/2024 07:05:19 am

That is correct to how the 2017 code reads to me.

Otherwise you would need a test pump to conduct a hydrostatic test, flow, or flush test on a manual system. But that's not a specific requirement.

Pipe from the fire dept. connection to the check valve is required to be hydrostatically tested at 150 psi for 2 hours every 5 years in accordance with the 2014 edition onward (13.8.5).

Reply
Jack G
12/4/2024 10:50:27 am

I agree with Pete. NFPA-25, 6.1 et al lists requirements for flow testing, checked up until 2020( 25 handbook). Forward flow only for automatic wet standpipes ( to check the flow and pressure at system flow)
I would also perform the 5 year internal for corrosion listed on the test page.

Reply
tamer
12/5/2024 07:10:45 am

this is correct
Since inspection of private fire service mains is not practical,
flow tests should be conducted at least every five years. Flow
test results should be compared to previous tests to reveal any
sign of deterioration of the flow and pressure in the system.
Should any deterioration be discovered, a complete investigation to determine the cause should be conducted.
Hydrants should be flushed annually by allowing full flow
for at least one minute. Dry barrel hydrants should drain thoroughly in less than one hour. During this procedure, hydrants
should be inspected for accessibility and operation, and hydrants should be lubricated. Inspection of standpipe systems should begin at the water
supply and continue throughout the entire system on a quarterly
basis. This inspection, as for that of a sprinkler system, should
reveal signs of damage, leaks, corrosion, or any condition that
may impair system operation. Where building occupant hose is
present, the hose should be removed from the rack or reel annually and inspected for evidence of vandalism. The hose should
be free of obstruction and not damaged by mildew or abrasion of
any kind. The hose should be reracked or rereeled in such a way
that folds do not occur in the same position on the hose. Standpipe hose should be removed from the system for hydrostatic
testing at five years and every three years thereafter.
Hose valves should be inspected quarterly to ensure that
the handwheel is not missing or broken, the threads are not
damaged, the valve is not leaking, and the cap is in place. In
cases in which high pressures are present, the valve should be
of the pressure-regulating type. Pressure-regulating hose valves
are generally of two types—pressure reducing, which controls
both static (nonflowing) and residual (flowing) conditions, and
pressure restricting, which controls residual conditions only.
Pressure-regulating devices should be flow tested every five
years to verify that the pressure-reduction setting is correct.
Valves that are not set properly should be reset; valves that are
not adjustable should be replaced.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT