I've got a high-rise project in a seismic zone higher than category C. We are required by IBC to have a secondary water supply other than the city supply (IBC 403.3.3). The structural team is pushing to not put the tank on the roof, and our site is extremely limited, so there is discussion about trying to bury the tank.
What pump/tank configurations are available for this situation? I am aware of either a concrete or fiberglass tank with a vertical turbine pump, but can you tie in the city supply to a vertical turbine submerged in a tank? Is there a way to appease this rule other than a secondary fire tank that I'm not thinking of? Thank you in advance for any help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Ken Thackery
5/5/2026 08:20:51 am
We just did one of these. The 40k gal tank is buried under the building- under the FP room- with a plate the VT sits on. There is also a secondary Horizontal pump per the owners reqirements being a hospital. The VT is the primary and delivers 100psi to the roof 14 levels up. Send me your email and I can send you pictures and data. You have to bring the supply into the room so I'm not understanding the question.
Reply
anthony
5/5/2026 08:28:05 am
Other tank configurations:
Reply
SShepherd
5/5/2026 08:58:37 am
All forms of tanks are available to you, but the key requirement is an "automatic" water supply. There will be questions on whether a suction tank with static volume or break tank. Tanks can be located within the building envelope at grade, above grade, or subgrade within the building footprint or beneath the building. All design options (pump and tank) are available, and all come with their own challenges. Highly recommend working with the water purveyor and the agency responsible for cross connection control as the water supply for the tank can come with its own challenges beyond the fire code or standard. Do not forget about the tank overflow if located within the building as the overflow needs to have a discharge point. I would highly recommend to not discharge the overflow within the building - try to discharge at grade. Coordination of a subgrade tank is very important and most likely will involve the structural engineer of the building. In my jurisdiction we have rarely seen alternatives to tank, as the water supply for the pumps must be reliable, and alternatives like the rooftop pool, or such just doesn't meet the reliability.
Reply
Jose R Figueroa
5/5/2026 09:56:20 am
I have observed the effects of minor E/Q on swimming pools. It's particularly concerning when they are located on the top floor. They can cause the building to sway. Disclaimer: I'm the FM or NFPA guy.
Reply
DJ
5/5/2026 10:41:21 am
If I understand correctly, you want to know how to eliminate a secondary tank and still satisfy the requirement of 2 separate water supplies, as required by IBC. I have successfully done this though involvement with the AHJ and their approval. In short, If the tank is sized to meet the demand and duration of the highest hazard, an auto refill, proven to refill at rate equal to the highest demand, it is the secondary supply.
Reply
Ron
5/6/2026 11:34:08 am
Another option we have used assuming it is large enough, is taking suction from a pool.
Reply
Anonymous AHJ
5/6/2026 12:04:19 pm
In our jurisdiction we have a situation similar to yours, a 10,000 gallon water tank was installed along with a water pump with a back up generator. The site is fully sprinkled and protected, the pump and associated piping is in an enclosed temperature controlled environment and what is exposed to the elements is insulated. No issues to date.