I wanted to get your thoughts on temporary fire pumps. We are in warm weather season here in MA, and a building wants to use a temporary fire pump to alleviate a fire detail that is on the building.
If this wasn't a high-rise, I honestly feel more inclined, but being that it is, I am more hesitant. I wanted to see if others have used them, and if so, what evidence did you bring to AHJs/Fire Depts? The client shopped around on their own accord and found an industrial end-suction centrifugal pump used for sewage bypass and general construction dewatering, which doesn't seem to be generally used for Fire Protection applications. Thanks in Advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
M.Newell
7/23/2026 08:09:11 am
There are companies that rent out listed fire pumps that are in connex or trailers that you can hook up to buildings. I would push for FP pump personally.
Reply
Jesse Cecil
7/23/2026 08:11:08 am
I'd have severe reservations about this. Anything used in fire protection, even temporarily has to be listed for such use. If this industrial pump is not listed for fire protection, it shouldn't be used. There are applications of course, where I've used tempeorary pump installations. But each time, the pump, controllers, etc have been adequately listed.
Reply
Chad
7/23/2026 08:11:36 am
I would require an FPE to sign off on whatever is going in. Obviously temporary non-listed equipment is better than nothing if it’s going to be out of service for an extended period of time
Reply
Glenn Berger
7/23/2026 08:24:29 am
1) I do not like anything that is "temporary" associated with a fire protection or life safety system. The question does not specify any type of duration.
Reply
Wes
7/23/2026 08:31:30 am
This sounds like at least a partially-occupied highrise, and looking to avoid Fire Watch. Without knowing the particulars it would be difficult to justify removing a Fire Watch by a non-listed, possibly non-automatic (certainly not to code) fire pump situation.
Reply
Ck
7/23/2026 09:02:40 am
I also don't understand why this pump is needed. Are you saying they dont have enough pressure so their sprinkler system is not working so theyre on fire watch and they want to use this pump to provide pressure so they dont have to do fire watch anymore?
Reply
Jack G
7/23/2026 09:50:47 am
Whether the temporary pump must be listed depends on the AHJ. They must review and approve the pump and the set up.
Reply
Jack G
7/23/2026 10:01:00 am
I use Godwin Diesel pumps which are in a conditioned trailer and come with all the hook ups and backflow prevention and hoses. . I normally supply the system thru the fdc similar to a fire department pumper truck. I then feed hoses from a hydrant for the supply. Or I Supply thru the existing test header . Rarely do I go inside and connect to the pump suction flange and spigot piece.
Reply
Mark Harris
7/23/2026 10:50:38 am
Was not cheap but in 2021 had lead time issues on a fryer water mist system pump and needed a temporary solution. Rented from Xylem. Trailer diesel. This was an industrial plant so temporary piping was much easier than a high rise basement pump. Here is link to what I think was the provider:
Reply
Ed Berkel
7/23/2026 11:15:45 am
As an AHJ, I would not approve that scenario as it is not listed for the application.
Reply
Kyle Wilcox
7/23/2026 12:12:32 pm
To meet NFPA codes you need either a "reliable waterworks system" or a single listed fire pump. In my opinion, a "reliable waterworks system" involves multiple pumps arranged for redundancy, and is designed for its purpose with an engineer's seal on the design.
Reply
Dan Wilder
7/23/2026 08:02:50 pm
We do this as a temp means when a fire pump is no longer working. This is an emergency service and the local AHJ requires full submittal of the existing fire pump and its rating, the temp pump and its rating, most pumps now carry a portable cell communication for monitoring, site plans for connections, estimated duration until the new pump is available, what the building is...it's several pages in total. They also require daily, or twice daily visual inspections, weekly pump runs, full documentation of the "ITM" to be available at short notice (often unannounced inspections). Full flow commissioning with pressure loss and manual startups once onsite.
Reply