Allow a Tank Fill Tee'd off the Building Fire Main?

2/4/2025

11 Comments

 
I'm working on an interesting scenario in which the client would like one main line into the building for fire and to tee off that line inside the building, with one line going to a giant indoor tank that holds 350,000 gallons.

It would be filled just one time per year. Assume 1,000 gpm for 6 hours that one time per year.

First - do you all see this as a possibility right off the bat?

We were talking about putting motorized valves wired back to FACP that shut off if the fire protection activates flow as a potential solution if it could work.

Initially I asked about a water tank for that until I learned it was 350,000 gallons.

Second - is it even possible to calculate out in that scenario?

One thing I love about FPE is the unique, always challenging scenarios that come up regularly. I'm looking forward to figuring out how we're going to handle this facility. Thanks in advance for any input.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
2/4/2025 07:34:50 am

It sounds like the tank isn't for fire protection. If that's the case, you'll need to meter the water coming into the building. So if you have a metered service, sure no problem, use a manual valve though so you know its closed when you're not filling it. In this case your system will be under impairment during the fill, a fire watch will be needed. This would be a combined service instance you may need 2 backflow preventers?

If there is no meter this probably won't be legal as you're not paying for the water. Also note the water won't be considered potable.

If the tank is for fire protection, then get a solenoid fill valve and a fill sensor (high/low/ fill line) as you would for any FP tank.

Reply
Josh
2/4/2025 10:12:21 am

It is not a tank for fire protection. It's a big enclosed tank for testing aquatic equipment. A very big tank.

I want to avoid multiple BFPs. All of this water is non-potable usage, thankfully.

As I mentioned in a reply further down in the comments, I'm told it's like 1/4th of a mile away from the town's large water tank and outbound pumping station and to expect "very high pressures and flows" at that location.

These are the feathers in the ol' cap at the end of the day. It's these different/unique questions and scenarios that keep me in this field. Lots of other engineers, even some I work with, just do the similar stuff with nothing at all unusual or very challenging on a regular basis.

Reply
Chad
2/4/2025 08:17:14 am

I am wondering what that tank is for too. Sounds like its not FP?

More and more water departments are not permitting combination FP/Non-FP services so they need to confirm they are not going to run afoul with the water authority as well.

Reply
Glenn Berger
2/4/2025 08:23:00 am

I agree that your scenario is interesting, but I have some questions that I need to ask to fully understand the situation.

Where does the FP portion of the system begin?

What is the purpose of this 350K storage tank?

Are there going to be procedures in place to terminate the filling of the tank, if a fire emergency happens?

One can interpret your question of can you use one tap from a water supply for two different purposes. If that is the case then yes it is possible.

Reply
Josh
2/4/2025 09:34:04 am

The tank is not for FP. It's for testing certain aquatic equipment. Think of them as enclosed raceways. I'm kind of in a spot here because the principal has proposed a solution then came to me and needs me to make it work, essentially. I have the same concerns the rest of you have but I'm also, like you all, a solutions guy and love a good challenge.

The solution to terminate filling the tank in a fire emergency, at this point in time, would have to be a logic controller that shuts the valve if the flow switch detects flow through the fire line.

The last sentence in your reply is one that typically I would say, sure this is kind of standard, but when you talk about the volume of water that needs to come through the non-FP line...now we are not talking about typical things I've seen happen before. This isn't your bathroom groups or something super run of the mill.

Reply
Jack G
2/4/2025 09:09:08 am

I m on board with questioning what the water is to be used for as it sounds like it’s not fire protection.
With this extremely large quantity ( not being fire protection) is it to be used for irrigation— hot climate?
Yes, connected to your fire system— non potable— then all the rules for non potable water supply in NFPA 13 apply— like return bend loops on pendent sprinklers.
The tank is too large I would think to be lined like used on fiberglass tanks used for domestic water.
Only opened for filling once a year is strange.
Agree this should have a water meter— and the pump incoming a turbo detector check valve as there usually a charge when water to the pump is used—- so a meter pit may be in order.

Reply
Josh
2/4/2025 09:37:24 am

Correct - it is not for fire protection. It's for testing marine equipment in an enclosure. It's one of those "oh, that's interesting" new things that comes up throughout one's career.

One of the rather interesting bits is the air relief of some sort to keep buildup from happening in this large enclosure. I'm either going to have to air gap it or put a proper relief on. Second interesting tidbit is I'm told it's like 1/4th mile away from the city's massive water tank and outbound pumping station and to expect "very high pressures and flows" from there.

It's going to be a neat one in the portfolio when all is said and done.

Reply
Jack G
2/4/2025 09:56:02 am

If used the way described above, the tank, with or without a pump for the testing of marine equipment—- the tank itself should be atmospheric and/ or have a vent( like in a fire tank) so a vacuum is not formed.
I would also use an appropriate clay valve vent ( for underground ) so that any trapped air in the underground is properly vented .

Jack G
2/4/2025 10:03:25 am

Atmospheric tank vent. Clay valve vents for underground piping systems. Additional venting as required when pumps are operating. I m concerned about vacuums being formed on both systems .

Reply
Franck
2/4/2025 10:33:48 am

Just a comment: what if the tank was located at a neighbour's place and he would fill it once per year from the city water supply?
You would not even know...
This is what could happen with city water supplies as they may supply other facilities/industries and deplete seasonally your available water flow and pressure.

The good thing in your case, is that you know when your system is not fully operational.
And you can react as for any impairment for the same water supply.

Providing some kind of "motorized valves wired back to FACP that shut off if the fire protection activates flow" could also be a solution. But if there are people attending on site when the water is used to refill the tank, you can also consider that those people could stop manually the filling operations (with some delays compared to an automatic interlock).

It is a potential threat. But only for a very limited period of time.
If I were the AHJ, I would probably accept it. But require a dedicated impairment procedure during this operation.

Reply
Jesse
2/5/2025 07:45:32 am

Yep, can be done. I've actually seen this before in LA or MS at a place supplying off-shore oil prorjects. The tank was a training dive tanak.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT