Allow a Maintenance Hose Upstream of Jockey?

12/24/2024

7 Comments

 
I have a project where the Specifying Engineer has noted to have a small hose connection for periodic (maybe every 6 months) building maintenance use to wash down a water intake filter.

They have specified that
it be fed from the jockey pump upstream of the jockey discharge check valve and connection to the fire pump connection, so it would seem that it would not really affect the fire protection system or fire pump discharge.

However, I don't think it is a good idea
, and I think a separate pump for building maintenance should be provided.

​Looking to see if there is any code reference I can use for backup as common sense doesn't always work or maybe I am wrong.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
12/24/2024 08:16:43 am

If I am reading your question correctly, the hose connection is downstream of the jockey pump, but upstream of the discharge check valve.

Sounds like there is no water pressure available for the minimal maintenance activities required. I do not believe that there is a violation of any NFPA standard here.

Consult with the appropriate municipality as this may be a violation of local regulations.

Reply
Piers Johnson
12/24/2024 10:16:41 am

Water supply is from a pond, it is a vertical turbine pump with a submersible jockey pump.

No concern with the water utility or metering.

Reply
Adam
12/24/2024 08:22:58 am

Where is the water drawn from? If from a Municipal system, Fire Protection water is not metered, at least not in my part of the world, and this set-up would basically be allowing the building owner to steal water by by-passing the meter for their own operational purposes, which I am positive the Municipality would not be happy with!

Reply
Daniel Ricker
12/24/2024 08:31:08 am

Jockey pump is not required per nfpa 20. It is a pump that is not required to even be listed. While not common, I have seen this approach used on industrial/larger sites before.

Taking water off of it would present no code issues, but may be a sticking point with the water utility if it is not metered.

Reply
Jose Figueroa
12/24/2024 09:37:04 am

NFPA 20 (2025)
4.27.1
For pressure-actuated fire pumps, a means to maintain the pressure in the fire protection system shall be provided in accordance with one of the following:
(1) A jockey pump
(2) A water mist positive displacement pumping unit in accordance with 8.5.7.2
(3)Another approved means that is not the main fire pump
4.27.2.2*
The jockey pump shall be sized to replenish the fire protection system pressure due to allowable leakage and normal drops in pressure.

Etc. Etc.

Reply
Jose Figueroa
12/24/2024 10:28:52 am

I apologize, but I am unclear about where the maintenance water originates in your question. I am also confident that the Authority Having Jurisdiction (AHJ) and the local municipality would not support this practice.

As a fire protection engineer, I learned that using water from the main fire pump system or any part of the fire protection system for maintenance purposes was prohibited. Once, I observed maintenance personnel using small fire hoses from the standpipe system, and the poor guys were fired.

However, practices evolve, Using water from these systems contradicts NFPA standards, as it undermines the integrity and reliability of the fire protection system. For detailed specifications, refer to NFPA 25, which outlines water-based fire protection systems' inspection, testing, and maintenance.

Reply
Jack G
12/24/2024 01:58:34 pm

As Mentioned above, the water supply is from a pond with a submersible jockey pump.
NFPA 20 has specific points to hit when setting the pump. Example the jockey discharge should be at least 10 psi higher than the fire pump. The capacity should be at least 1% of the fire pump and if the underground mains are pressurized the capacity should take into account additional gpm s for leakage.
The submersible jockeys have a curve that allows different pressure variations. ( I nicknamed them “ infinity “ pumps 50 years ago. ) so care should be taken with the wiring and voltage.
Most install into pvc sleeves to keep the motor from overheating.
For a pond installation we would build a sizable sump with shaker screens to cut down on clogging ( for both pumps)
From memory the wiring that is connected to the submersible is what they call a “ water proof “ connection, and that connection was not ul listed or approved. ( I recall many discussions with the AHJ electrical inspectors)
The jockey discharge should have a properly sized relief valve. ( after the check and before — after to relieve pressure build up when using the proposed service valve before the check )
The jockey pump is classified a maintenance pump and needs no listing. However the controller and wiring does.
With that said a valve tap before the check- with the required relief valve ) could be added for pump room screen, sump screen maintenance and hose down of the area.
A pressure regulator might need to be added to the service hose as a fire pump / jockey pump is usually a high pressure and whatever you are cleaning could be damaged. A lot of “ screens/ louvers “ have a max 90 psi for cleaning with a pressure washer, which in essence is what the engineer is trying to do.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT