|
Do all wet systems require an FDC?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/13/2025 06:18:19 am
From NFPA 13 (2016 Edition):
Reply
Anthony
6/13/2025 08:18:01 am
Pete got the code section right here. I'd also add its a should provide regardless of the the exceptions.
Reply
Glenn Berger
6/13/2025 08:22:51 am
The key words in the code is "shallv require." I would still consider providing the FDC in case 3.
Reply
Glenn Berger
6/13/2025 08:23:57 am
"Shall not require" -- stupid thumbs!
Reply
Todd E Wyatt
6/13/2025 08:25:08 am
The FDC requirements start in the scoping Code (e.g. IBC-2024) which then references the "NFPA standard applicable to the (sprinkler) system design".
Reply
Wes
6/13/2025 08:25:21 am
The question doesn’t name 13 vs 13R or 13D. NFPA 13D systems do not require FDCs.
Reply
Robert Hughes
6/13/2025 09:05:31 am
Though rare, AHJ sanctioned imited area systems, installed extraneously, typically do not have FDCs either.
Reply
Ryan Jacob Geer
9/15/2025 10:14:06 pm
Incline village Nevada, North lake Tahoe fire , Douglas county fire all require FDCs on Houses 13 D .
Reply
Jack G
6/13/2025 12:47:02 pm
An FDC is always a good idea whether required or not, even a minimal one where they are not required.
Reply
James E Art Fire Protection Engineer (FPE)
6/13/2025 03:42:48 pm
Balance cost with whether it adds safety!
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
