What are others doing to combat Microbiologically Influenced Corrosion (MIC) in their sprinkler systems?
I'm dealing with a project where MIC has been found in a nearby building/system. Doing research, nitrogen appears to be a popular treatment method, but I've read sprinkler-based articles that it's not effective. I also noticed that the NFPA 13 2025 edition removed the treatment options previously in paragraph 5.1.4.1.2. Additionally, the client does not want the monitoring option (item 3 of 5.1.4.1.2, 2022 edition). Any advice on how to prevent MIC here? Thanks in advance. Moderator's Reminder: The intent of the forum is for clear, substantiated, and helpful conversation. Comments which do not meet the community guidelines will be removed. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
6/30/2026 06:05:56 am
Have you looked into General Air Products' "Vapor Pipe Shield"?
Reply
Wes
6/30/2026 08:14:59 am
I'd be curious to check out about articles on nitrogen not being effective. It has a track record, is used even by larger users and FM recommends it.
Reply
Brian Gerdwagen
6/30/2026 09:09:28 am
Not all corrosion, even microbial, is aerobic. A lot of the corrosion found is anaerobic and oxygen does not play a part.
Reply
EL
6/30/2026 08:22:02 am
If it is a wet pipe system, eliminate trapped air.
Reply
NK
6/30/2026 08:25:36 am
Flush the system, add vapor pipe shield, if it's a wet system add automatic air vents at system high point(s). Nitrogen is only effective if it can be maintained at 98% or higher which is difficult to achieve (especially in older systems) which is why there's growing concern with it's application.
Reply
Wes
6/30/2026 08:37:25 am
The downside I'd have with Vapor Shield is having to add an RPZ to the system - but the viability concern is there too - getting coverage in all the smaller diameter branch pipe. Not saying nitrogen should go everywhere, at all. If the system is small enough, the cost of nitrogen might be more than just replacing the pipe or portions of the system regularly. At least with the nitrogen systems you can see the % nitrogen actually achieved (I think all vendors do that now?). I could be wrong but I dont believe the Vapor Shield has a way to monitor/prove that it has coverage in those branch pipe dead ends.
Reply
Glenn Berger
6/30/2026 08:32:17 am
The issue concerning N2 stems from the difference when using 95% design vs 97% and above design levels.
Reply
Wes
6/30/2026 08:38:51 am
Right - for a MIC concern specifically this could be the easiest/cleanest route if that's viable. Or even start with that and then test for MIC periodically?
Reply
Dan Wilder
6/30/2026 10:03:03 am
Living in the desert, our water quality is very poor (lots of chlorine, calcium, and other hard water aspects) and we deal with many issues generally linked with the water quality. However, there are a lot of other factors that play into things.
Reply
Jose Figueroa
6/30/2026 10:54:43 am
The latest update from FM is that MIC is an overrated source of corrosion. Consider MIC only as a contributing factor—prioritize oxygen control (vents + nitrogen where feasible), thorough inspections, and physical removal (replacement) over chemical treatment. This advice is conservative and evidence-based, focusing on long-term system reliability without creating new risks from uneven chemical application.
Reply